Bruce
Member Posts: 27
Is the taco vortex an air scope or more like a spirovent.I guess is what a want to know is does the vortex need this 18" straight run before it can work properly.
Thanks Bruce
Thanks Bruce
0
Comments
-
According to Taco
"no minimum length of pipe required after bend or elbow"
and they say no more than 10 ft/sec flow rate. Hope this answers your question.0 -
Thanks Eric
What does that equal to in a 3/4 copper pipe @ 2-3 gpm
Bruce0 -
-
I may be wrong but
I think 10 ft/sec using 3/4" pipe comes out to 15gpm, but you might want to wait for someone else to post a reply.0 -
-
If i only run 2 ft/sec.
will the vortech still work Bruce0 -
Yes, It will work
Yes, It will work. The max ft/sec is based on the ASHRAE recomendations for velocity noise not the effect on air separation.
- Mark Chaffee
Taco,Inc.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements