Anyone know why a thermostat might only work intermittently?

Options

Hello! I’m hoping someone might have some idea of what’s going on with my thermostat.

I’ve lived in my apartment unit for a little over a year now and had no issues with my ac or heating until this past spring when my old thermostat stopped working. The maintenance guy came and replaced the wall unit with a new model. A few days after that the AC started having issues again and wouldn’t click on, but the issue was only occurring sometimes. This went on for a few weeks with apartment maintenance unable to figure out the issue until finally a contractor came out and messed with the settings and set the thermostat to hold. It worked keeping the unit on hold mode all summer with just manually adjusting the temp rather than setting a schedule.

I recently went on a week long trip so I turned the thermostat off. When I got back it was cold enough to need the heater. Low and behold I’m having the same intermittent issue, now with the heater not clicking on for multiple hours a day, then randomly working again for a few hours before not working again. I tested it and when the heater won’t click on, the AC also won’t turn on, so I’m pretty convinced it is an issue with the thermostat in some way, but am happy to be proven wrong if it’s something else that can be fixed.

If anyone has any ideas about what might be going on, I would really appreciate the help. Thank you so much! Here is a photo of the thermostat unit:

IMG_5736.jpeg

Comments

  • mattmia2
    mattmia2 Posts: 18,493
    edited 1:46AM

    what makes you think the problem is with the thermostat? it looks like the thermostat is making a heat call but the equipment isn't turning on.

  • Jamie Hall
    Jamie Hall Posts: 28,038

    Does the thermostat have batteries? If so, are they fresh? The display seems to suggest that it does, and the batteries are good, but I need to ask.

    When you notice the thermostat misbehaving, what does the display say? (for example, in your photograph, the set temperature is 68 and the room temperature is 64, so it should be calling for heat — and indeed the display says that it is calling for heat. Was, in fact, the heat running at that time?)

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • t18t18
    t18t18 Posts: 5

    I’m assuming it’s the thermostat because the issues began when it was replaced and are occurring for both the heater and the ac, also because the maintenance people came checked the physical units and said they looked fine. That being said I am not at all an expert so if this sounds like a specific issue I’m definitely willing to check it out!

  • t18t18
    t18t18 Posts: 5

    thank you! Yes, the batteries are fresh and that is a photo from when it was misbehaving, so when I took that photo the heat was not running. It also looks like that when the heater is working though.

  • ratio
    ratio Posts: 4,355

    I've run into similar problems (erratic operating even though the stat looks right), it ended up being a loose connection, the wire was tucked behind the screw clamp on the thermostat base & not under it. It looked right!

    Pull the stat off the base, then tug on each wire individually. They should be in there firmly.

    mattmia2
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,052

    Who pays the heating bill? Is the heat included in the rent or do you get a separate electric and/or gas bill?

    If the heat is included in the rent, then there is a possibility that your landlord has a second control system that can disable the heating an cooling unit at certain times of the day to reduce the energy cost. If that is the case there is little you can do about it, unless you can get the authority having jurisdiction to come to your apartment and document the information you have presented here. In New Jersey that would be the local department of health. In New Your City the NYC Department of Housing Preservation and Development handles those complaints. Outside the city in the rest of the state might be the local building code enforcement department.

    I have been involved with disputes like this in NJ and have testified in court on such matters as an expert witness. Lets hope it does not get that far.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    t18t18
  • 109A_5
    109A_5 Posts: 4,820

    Not really convinced "The maintenance guy" actually repaired the actual problem. Or replaced one problem with another.

    You need to prove it is the system and its wiring or the thermostat.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • t18t18
    t18t18 Posts: 5

    Hi, thank you! How would I go about proving this? Sorry I do not know anything about heating systems or thermostats. Thank you for your advice!

  • t18t18
    t18t18 Posts: 5

    thank you so much! I will try this and see how it goes!

  • mattmia2
    mattmia2 Posts: 18,493

    you say the old thermostat stopped working. are you sure that was the t-stat and not the equipment and the equipment either got rest or coincidentally started working when the t-stat was replaced?

    the test is to jumper the wire the t-stat closes, first at the t-stat, then at the equipment if it is still intermittent jumpered at the t-stat.