Shut off not working properly

Options

oiler & Control: Utica PEG187AS gas-fired steam boiler with a McDonnell & Miller Series 67 low-water cut-off, just installed a brand-new M&M 6667 (153825) replacement head.

2.

Terminals 1 and 2 are on top and wired to the burner circuit.

Pulling one wire off Terminal 1 stops the boiler from firing (so the circuit isn't bypassed).

Opening the LWCO blow-down valve produces a strong rush of water and empties the sight glass, yet the burner stays running.

Comments

  • mattmia2
    mattmia2 Posts: 18,459

    need to clean out the body of the lwco, the float is hanging up on the debris inside it.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,379

    Make sure the switch is installed with 1 & 2 on top. factory might have screwed it up. Possibly a bd switch but what @mattmia2 said is more likley.