Shut off not working properly
oiler & Control: Utica PEG187AS gas-fired steam boiler with a McDonnell & Miller Series 67 low-water cut-off, just installed a brand-new M&M 6667 (153825) replacement head.
2.
Terminals 1 and 2 are on top and wired to the burner circuit.
Pulling one wire off Terminal 1 stops the boiler from firing (so the circuit isn't bypassed).
Opening the LWCO blow-down valve produces a strong rush of water and empties the sight glass, yet the burner stays running.
Comments
-
need to clean out the body of the lwco, the float is hanging up on the debris inside it.
0 -
Make sure the switch is installed with 1 & 2 on top. factory might have screwed it up. Possibly a bd switch but what @mattmia2 said is more likley.
0