What parts should I add-on my new peerless 63 06 steam boiler

Options

First I want to thank everyone for their awesome help With the boiler and the piping.I've already Ordered the safety guard to replace the cycle guard. And I ordered the VXT. I like the idea of the 67 where I can go down and flush it every couple weeks And cleaning once a year instead Of just cleaning once a year.I'd appreciate your thoughts on this and if there's anything else you think I should be adding to this. It was the knockdown package so the only thing that was supposedly needed was the VXT. I started a new Post because it was for the parts. If it was the wrong thing to do just let me know thanks. And should I also get that upper tube assembly or is that something that the installer should have readily on hand.

Screenshot_20261117-183046_Samsung Browser.jpg Screenshot_20261117-180447_Gallery.jpg Screenshot_20261117-180313_Gallery.jpg Screenshot_20261117-180043_Gallery.jpg

Comments

  • Jamie Hall
    Jamie Hall Posts: 28,010

    Looks good. I like the 67 LWCO — not everyone does. And yes, I'd order that upper tube assembly. You CAN make one yourself, but it's so much easier…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Posts: 4,790

    Well if you are going to use the M&M 67, you may not have to touch it for many years (other than Blow Downs). At some point you may need to replace the Blow Down valve or you can add a full port ball valve after it. Water treatment may slow down the rusting.

    Spare gaskets are handy. I used the paper OEM style gaskets as a template and made reusable gaskets out of silicone rubber sheet material, no more gasket scraping.

    I would remove the screws (Red arrow) one at a time and apply Never Seize to them, so when you need to get them out you can. My M&M 67 has over 50 years of service with minimal maintenance.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030

    The new #67 LWCO comes with the ball-valve blowdown, so there is no need to add that to the list right now. Your Peerless comes with an electronic LWCO, so you may not need another electronic one since you already have one installed.

    The water feeder is a nice feature for hands-free operation over extended periods. If you happen to run low on water while you are away, the water feeder can take care of that for you.

    Just don't get lazy and forget about the weekly blowdown and other weekly inspections that should be performed. Having an automatic water feeder does not mean you should stop monitoring how much water is being added over the course of the heating season.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Posts: 18,453

    in fact it is a great idea to put a water meter in the makeup water feed.

  • Steve214
    Steve214 Posts: 23

    I see no reason to install a 67. They are expensive and the quality is not what is was in the past. The #11 switches fail and are not cheap. Use the probe style and replace the probe every 5 yrs and your good to go. You can also pull the probe and clean it. I prefer a manual feed with a meter but the VXT is pretty good.

    GrallertKC_Jones
  • AdmiralYoda
    AdmiralYoda Posts: 818
    edited 2:47PM

    For a steam enthusiast and someone who keeps the maintenance at 100%, I'd consider the 67 LWCO. But really, a probe type is probably a better choice these days.

    My Peerless is 41 years old and has the original 67. Zero maintenance was done until I bought the house 18 years ago and shortly after I learned about steam I realized my LWCO was stuck in the "up" position.

    I did weekly blowdowns to clean the gunk out, which there was always plenty…. but I didn't know of the "safety" check while doing the blowdown. Not only is the blowdown important to clean the muck out but also to make sure the boiler shuts off when the float goes down.

    After learning this….I pulled it apart, cleaned out the build up and put it back together with new gaskets and it was back in action. I've since been using Rectorseal 8-way to prevent corrosion, of which I have zero. No rust or muck build up anywhere in the boiler, including the LWCO.

    If you are someone who is mostly "hands-off" and the only time the LWCO see some love is during the yearly inspection….I'd go with a probe type. If you plan to play with and tweak your boiler weekly (like @ethicalpaul) an LWCO isn't a bad option.

    That said…if I were to replace my boiler today I'd go with a probe type. Easier to clean and maintain and if something goes wrong….much cheaper and easier to swap in a new one.

  • BobC
    BobC Posts: 5,581

    if you have a 67 you need to think seriously about using SteamMaster or 8 way ti get the PH up to 9 or more. That will get rid of corrosion and make everything happier, my 13 year old Smith boiler still has clean rust free water in it, I've used SteamMaster since it was new, I throw a tabket in every 3-4 years to keep that PH up..

    Bob

    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • bkdymc
    bkdymc Posts: 29

    Thanks for all the great feedback! I have to make one clarification that I didn't make. The boiler is not installed yet it will be started on Monday.

    The VXT Monitors the water that's being fed.

    It also has the programable Delay So I can eliminate the cycle guard which it seems many here do not like and I can replace it with the safety guard. Then I add the 67 which will help keep the boiler cleaner with the weekly flushdowns and also has the backup low water cutoff that can be tested weekly is that correct. Now swapping out the Cycle guard with the safety guard that shouldn't be an issue correct is there any extra parts that I should have on hand in order for them to do that. The VXT is a standard part so that should be okay. Since the 67 isn't Normally installed with the other 2 is there a certain way that they should be installed So they work best together and one doesn't interfere with the other? I don't know if there's different ways but at least I'll have an idea when they go to put them in. Now the VXT says it has a strainer. Would you recommend a separate inline strainer also and if so is there a certain type or brand that you recommend. I see several installations with what looks like a pressure troll and an aquastat Is there an advantage to having both and if so is there a certain type or Brand that you recommend. As you can see I don't know too much but I'm trying. I can only imagine where I would be right now if not for your help. Thanks again.