Thermostat Wiring Question

Options
gcdchico
gcdchico Posts: 7
edited November 15 in THE MAIN WALL

I'm a new person trying to learn my system. We recently move to a new home that has 3 zones and radiant floor heating. I trying to connect the floor heat in one zone currently. That zone has the thermostat pictured below. (having problems with posting my picture)

B is connected

G Y W R are connected

My old Honeywell thermostat RTH2300b1038 is connected to a TACO SR503 switch.

Will this connection drive my hydronic floor heat system? When I increase the Honeywell temp setpoint (+2 degrees) the Taco turns on the Buderus boiler and the Taco zone indicator lights. However the HVAC fan also turns on and that confused me — I believe this thermostat will NOT support both HVAC heat and floor heat. I ended the test before getting any HVAC heat because I was worried about damaging transformers or something else.

What's my next step?

Upgrade my thermostat? Let the thing run and hopefully the floor will heat? Disconnect the yellow fan wire?

THANK YOU!

Thermostat .pdf

Comments

  • ethicalpaul
    ethicalpaul Posts: 9,098

    Here's the picture from the other thread:

    image.png

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,778
    edited November 15

    Do you have a heat pump ?

    Another option is someone may have wanted air flow with the radiant heating so they repurposed the Orange wire to command the blower on during heat. I'd be curious what the thermostat wires are connected to at the other end.

    You could move the Orange wire from the "B" terminal to the "O" terminal. Or just disconnect the Orange wire at each end. If you do any wiring changes turn the power off to the system when making changes.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,996

    Your main question "Will this connection drive my hydronic floor heat system?"

    Depends

    If the R on the thermostat is connected to the R on the Taco SR503 and the W on the thermostat is connected to the W on the SR503 then the hydronic floor heat should operate if that zone you connected the wires to operates the floor heat circulator pump.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?