Thermostat Wiring Question
gcdchico
gcdchico Posts: 7
edited November 15 in THE MAIN WALL
I'm a new person trying to learn my system. We recently move to a new home that has 3 zones and radiant floor heating. I trying to connect the floor heat in one zone currently. That zone has the thermostat pictured below. (having problems with posting my picture)
B is connected
G Y W R are connected
My old Honeywell thermostat RTH2300b1038 is connected to a TACO SR503 switch.
Will this connection drive my hydronic floor heat system? When I increase the Honeywell temp setpoint (+2 degrees) the Taco turns on the Buderus boiler and the Taco zone indicator lights. However the HVAC fan also turns on and that confused me — I believe this thermostat will NOT support both HVAC heat and floor heat. I ended the test before getting any HVAC heat because I was worried about damaging transformers or something else.
What's my next step?
Upgrade my thermostat? Let the thing run and hopefully the floor will heat? Disconnect the yellow fan wire?
THANK YOU!
Thermostat .pdf
    ethicalpaul Posts: 9,098
    Here's the picture from the other thread:
    109A_5 Posts: 4,778
    edited November 15
    Do you have a heat pump ?
    Another option is someone may have wanted air flow with the radiant heating so they repurposed the Orange wire to command the blower on during heat. I'd be curious what the thermostat wires are connected to at the other end.
    You could move the Orange wire from the "B" terminal to the "O" terminal. Or just disconnect the Orange wire at each end. If you do any wiring changes turn the power off to the system when making changes.
    EdTheHeaterMan Posts: 12,996
    Your main question "Will this connection drive my hydronic floor heat system?"
    Depends