Head Loss Headache

Options

Comments

  • Jamie Hall
    Jamie Hall Posts: 27,967

    Presumably you have the proper test equipment to perform all the startup sequence?

    Without knowing a lot about the rest of the system I wouldn't care to specify a pump speed…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Posts: 28,678

    which boiler do you have? Which circulator? What size boiler piping?

    Some answers in this chart.

    IMG_1764.jpeg

    What temperature are you running the boiler? With a wider delta, slower pump speed, you may put the boiler in Condensing mode, return below 130. Which increases efficiency

    The manual may indicate the widest delta, sometimes 30 35 degrees is allowed in fire tube boilers.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    ScottSecor