Head Loss Headache
Options
scatgo
Posts: 99
With the information in the links would anybody be able to tell me if i should run the pump at speed 1 2 or 3 for the primary loop?
0
Comments
-
Presumably you have the proper test equipment to perform all the startup sequence?
Without knowing a lot about the rest of the system I wouldn't care to specify a pump speed…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
which boiler do you have? Which circulator? What size boiler piping?
Some answers in this chart.
What temperature are you running the boiler? With a wider delta, slower pump speed, you may put the boiler in Condensing mode, return below 130. Which increases efficiency
The manual may indicate the widest delta, sometimes 30 35 degrees is allowed in fire tube boilers.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1