Aftermarket Outdoor reset wiring and return bypass questions
I am thinking about getting single stage outdoor reset to add to my home gas boiler hydronic system. I am very familiar with low voltage and electrical wiring, but relatively new to boilers since moving to this house. Looking for some confirmation this will work ok with my setup
Background:
Peerless Boiler MI.05.SV.WPC-05 boiler. Non-condensing 115,000 DOE BTUs Natural Gas. Installed 2004
Cast iron radiators all in one zone with a circulator. Circulator is on the hot side, just after the expansion tank and automatic air bleeder
130degree recommended min return temp per boiler manual
Bypass with ball valve installed from just before return input to just after heater water output, before the expansion tank and circulator
There is no heated water storage tank
1925 foursquare 2-1/2 story, approx 2200 sf heated space. Stone foundation and first floor walls, wood frame upper floors. typically layout. Living room, dining room, kitchen foyer and power room on first floor 2 bedroom/2 bathroom and office on second floor. single bedroom/bathroom on 3rd floor. Partially finished basement with no radiators
New(er) everywhere windows. Decent roof insulation, plaster over lathe walls with no insulation
Climate Zone3 in suburban Philadelphia. Average low temp January is 26F
We keep the house chilly indoors in winter by choice, around 63F
Existing Controls:
Honeywell Aquastat L8148E with Honeywell Home RTH6360D1002 thermostat
B1 output is connected to electric damper which actuates when thermostat calls for heat, then when damper fully open, triggers the gas valve which fires the pilot light and burners
Max temp cutout set to 180F
we generally keep the thermostat at single setpoint all the time, although sometimes will do a slight 1 or 2 degree setback overnight when it isn't really cold out so the radiators kick on in the morning to warm things up a bit getting out of bed.
A few questions
  1. Considering this outdoor reset unit, Tekmar 256 (https://www.watts.com/products/hvac-hot-water-solutions/controls/boiler-and-mixing-controls/256) single stage looks like an affordable option. Installing the outdoor temp sensor and output hot water temp sensor is simple enough However, the installation manual doesn’t have a typical connection and ladder diagram to show where it fits into a system. https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/81348-source/639223626220000000/256-d-09.pdf
    How should the boiler demand input on the Tekmar be wired into the existing aquastat setup? Do I tee the existing thermostat call for heat T terminal to the Tekmar Boiler demand, and insert the Tekmar boiler contact closure between B1 output on the aquastat and the blue wire to the electronic damper? See diagram.
  • Thinking about how the control signals would flow, this seems to make sense
if the T-stat calls for heat, T goes low and the aquastat will trigger the circulator relay.
When the outdoor reset sees the boiler demand signal from T go low, it will evaluate the outdoor temp and boiler output water temp sensor inputs and decide whether to fire the boiler or just circulate the hot water.
When the outdoor reset boiler relay closes, connecting B1’s 24vac to the damper, the actuator will open, then provide 24v to the gas valve to light the pilot then the burners
When the boiler water satisfies the Outdoor reset sensor, the boiler relay will open stopping the burners and closing the damper. And the circulator will run until the thermostat is satisfied or until the Outdoor reset demands the boiler again
  • If instead I wired the thermostat T wire only to the Tekmar demand, the circulator wouldn’t run unless the tekmar demanded the boiler, so no hot water would be delivered to the radiators when the Outdoor reset is satisfied with the boiler water temp. which doesn’t make sense.
2. For 24vac power for the tekmar, I’d pick up 24V at terminal Z and Common at Tv or B2. The transformer on the aquastat looks pretty hefty so thinking no concern with a 2VA load per the Tekmar spec sheet
3. I am not sure when/how to adjust the bypass ball valve. If I run the system now with the bypass valve closed, the bypass piping just before the T where it joins back to the hot water output from the boiler (green arrow) is warm/hot. However as soon as I open the bypass a little, that point gets cold, which indicates to me that cold return water is flowing around the boiler input and cooling the output water. But I thought the idea is that hot water from the boiler output should be pulled the other way to warm the input side of the boiler? There is no check valve so water can flow either way.
I have a good DVM meter with a temperature sensor that I could tape the black iron boiler input pipe and experiment to see how to get to steady state > 130F. is that the best approach? How long do I let the system run before measuring and adjusting?
Also since this is a manual valve, I suspect I will need to adjust the valve to different settings for the shoulder heating season vs the coldest part of winter? What would be practical, to find one shoulder season valve position and one cold weather position, and just switch at some point when it get cold enough? or will I be able to find one setting to work all the time?
Thanks for any assistance. some pics below for reference.
    hot_rod Posts: 28,790
    just one thermostat? That wires to heat demand, it picks up 24 v frim the transformer you connect to
    5&6 to boiler tt
    Yes the ball valve bypass is a manual setting, a static device on a dynamic system.
  • dmxart
    dmxart Posts: 5
    Thanks for the diagram
    What it is missing is the circulator aspect of the system. with what I have, if I connect my thermostat to the Tekmar bolier demand, and then connect 5&6 to aquastat/boiler Tv & T, the circulator will only run when the Tekmar calls for heat.
    So if the tekmar processor says max water temp should be 150F, when that is reached on the output pipe temp sensor, it will kill the burner AND circulator even if the thermostat is still calling for heat. and with the circulator off, the only room heating will be the non-circulating water that happens to be in the radiators at the time.
    that doesn't sound right to me. shouldn't the circulator keep running until the thermostat is satisfied and distribute remaining heat from the boiler?
    I'm sure in new condensing boilers, the fancy processor can control the circulator and burner separately, or somehow modulate the burner output to achieve a lower temp while still running the circulator. But since this is older non-condensing with single on/off for everything, maybe I am just thinking about it wrong?
    Is the circulator controlled by the boiler contact now? Does it run after the burner is off? Nothing would change if that is the case. Or is the pump controlled by some other means?
    Jamie Hall Posts: 28,006
    The whole fundamental idea of outdoor reset is to control the circuiting water temperature at just the right value to provide for the heat loss of the spaces. All the time. So you have one circulation system, powered by one or more pumps, and the temperature of the water being pumped is controlled by the outdoor reset.
    Now you also have a power — heat — supply; in this case non-condensing, non-modulating, fixed output boiler. That's fine. What that means, though, is that the boiler doesn't have to run all the time to supply the load. Sometimes on, sometimes off.
    OK. How do you control this? The most effective method is primary/secondary pumping, or, a very similar alternative in terms of logic, a buffer tank. The heating loop, with its own pump, is constant flow, and has a modulating mixing valve on it, controlled by the outdoor reset,, which mixes return water from the loop with the hot feed water from the boiler in just the right ratio to make the water being pumped into the radiation the right temperature. The rest of the return water is sent back to the boiler, where a second pump pumps it through the boiler and back to the takeoff for the system. That loop is controlled by the boiler's aquastat, which will fire up the boiler when the return water coming to the boiler drops below 140 F (some say 130 F, I prefer 140 F for corrosion protection).
    This is preferable to a modulating bypass, as that has no way of controlling the temperature of the water in the radiation — only the flow — which makes balancing very difficult.
    A fixed or manual bypass is virtually useless. Like a stopped clock, it is correct only for one specific condition.
  • dmxart
    dmxart Posts: 5
    you are correct. right now, when the thermostat calls for heat, the circulator is started by the aquastat along with the burner. and when the thermostat is satisfied, the both burner and circulator shuts off.
    although it seems the same, the difference is that in the current model, the thermostat is satisfied when the boiler shuts off. if you add an outdoor reset, the reset supply sensor could be satisfied before the thermostat and the boiler will be off with the radiators giving off their stored heat. Until the water at the sensor drops below the restart temp and refires the burner and circulator, or the stored heat in the radiators satisfies the thermostat. which maybe is enough since it may reduce overshoot.
    I don't have issues with short cycling now where the boiler reaches the high-limit and kicks off before the thermostat is happy. But I do have some short cycling I think caused by the thermostat, which even though it is in boiler/radiant mode, still calls for heat more than I think it should.
    Since boiler is older noncondensing/nonmodulating, and only have a high-cutoff aquastat, and don't have storage tank, my options without major replumbing work seem very limited.
    add reset
    do nothing
    tweak thermostat to Boiler/Steam mode
    Saving the $250 that an outdoor reset will cost isn't must of a stretch. potentially with some increase in comfort.
    I think the call to TT stays on until the thermostat turns off the tekmar. The boiler burner will cycle off temperature if the boiler aquastat or the tekmar is making the call.
    So I believe the circ runs until the heat call satisfies.
    109A_5 Posts: 4,790
    edited October 30
    Having the Tekmar's terminals 5 & 6 control the Boiler's T-TV of the L8148E Aquastat (where the thermostat was), that will shut off the circulator when the Tekmar releases the contact closure at terminals 5 & 6.
    A contact closure between T-TV energizes Relay coil R, this closes contacts R1 (Circulator) and R2 (Vent Damper then Burner).
    So Interrupting the B1, High Limit, R2 circuit as the @dmxart originally had it is one way to avoid circulator shut down during a thermostat call for heat at the expense of cycling the Damper a lot as the Tekmar modulates (duty cycles) the Burner to control water temperature.
    109A_5 Posts: 4,790
    edited October 30
    I think I would do it this way. It checks all the boxes for me. Sadly it needs a relay. Probably could do it without the relay and the extra transformer but that may be more risky.
    Tekmar is on its own power source.
    Circulator and Vent Damper are 100% active during the thermostat's call for heat (Demand).
    The Tekmar's Boiler Control terminals 5 & 6 controls only the boiler's burner.
    In this case with the added relay which draws current from the L8148E's transformer when active, I would use a small relay with the least amount of coil current draw you can find.
    109A_5 Posts: 4,790
    edited October 30
    This may work too, but load of the Tekmar is on the L8148E's transformer.
    109A_5 Posts: 4,790
    The thing that seems odd to me with the Tekmar 256 is which is the actual thermostat ??? Use an internal sensor or the demand input. Do you set the internal a few degrees above the thermostat connected to the demand input ? Would that bias the Reset curve ?
    If you simply set the Demand input to 100% how do you control the circulator and the burner independently ???
    If a thermostat is connected to the Demand input, what do you do with the internal thermostat settings? Also it makes the circulator control weird with the unoccupied temperature control (Tekmar 256 as the thermostat).
    The more expensive units have independent burner and circulator control.
    To me the Tekmar 256 seems like an awkward, half baked product. Maybe I'm missing something.
    109A_5 Posts: 4,790
    HVACNUT Posts: 7,815
    You're not breaking TT or RW at the aquastat from 5-6 N.O. on the Tekmar. You're going to break B1. The burner circuit will open while the circulator continues to run if there's still a heat demand.
    You're system is piped as a boiler bypass.
  • dmxart
    dmxart Posts: 5
    edited October 31
  • dmxart
    dmxart Posts: 5
    Thanks all.
    @109A_5 's diagram 2 is where i am leaning
    L8148E's label says max 1.2A (1.4A if controls < 77F which they always are)
    The gas valve is 200 mA steady state and 1.25A at ignition
    add on another 125ma for the tekmar. Which makes peak load at ignition 1.375A, which is only about 5 seconds every burner cycle
    direct wiring is just within the 1.4A specs for 77F ambient temp. If I can find a low coil load transformer, then could do diagram 1, otherwise it is a wash.
    109A_5 Posts: 4,790
    edited October 31
    Let us know how the internal to the Tekmar 256 thermostat versus the boiler's thermostat situation works out.
    I've used that tekmar for many years, powered from the boiler transformer, wired to TT. Don't over-think it :)
    109A_5 Posts: 4,790
    So how do you set the TWO thermostats ???? The instructions show an internal thermostat setting and you also can use the Demand input as an external thermostat.
    If the Boiler control terminals (5, 6) are wired to the boiler's T-T how does the it control the Boiler's water temperature and room temperature ? Some Psychic network with the Boiler's burner ?
    I don't see how this thing does anything actually more productive than a plain old thermostat. The more expensive Tekmars make more sense, since they have independent Burner and Circulator control.
    The OP indicated 1 zone, I assume 1 thermostat?
    I see one circulator, looks wired to the boiler.
    No psychic network required.
    Receive the control, wire as shown and report back
    109A_5 Posts: 4,790
    1 + 1 = 2
    This is one thermostat, internal to the Tekmar 256.
    The other (original to the home on a wall) would be another and connected to the Demand terminals per the instructions.
    This is a perfect example why folks hate reading the instructions, they don't make any sense.
    109A_5 Posts: 4,790
    edited November 1
    So how do you regulate system's water temperature independent of the room temperature, using 'Outdoor Reset' with just one T-T control that controls BOTH one circulator and one burner that are either On or Off at the same time????
    If you can't independently control the system's water temperature, what is the point of a controller with 'Outdoor Reset' ????
    with the info we have, I assume the single circ is controlled by the boiler relay. Could be run by a relay box.
    So the wall thermostat keeps call to the tekmar, burner and pump run until the call satisfies.
    The tekmar just becomes the boilers operating temperature control
    OCC or UOCC setback functions
    Yes the more $$ tekmar gives you multiple outputs.
    This basic version is probably the same”brain” as used on the Taco I valves with ODR function.
    This 256 has been around since 2000. It was seen in various colors as OEM product as I recall.
    109A_5 Posts: 4,790
    edited November 1
    With Tekmar 256 other than approaching design outdoor temperatures it seems to me that modulating the whole Boiler what you will save in fuel you will spend in maintenance, especially if you have to pay someone to do the maintenance.
    I would think keeping the circulator running and the damper open during the whole call for heat and just modulating (Duty Cycle) the burner would be better.
    Then the OCC or UOCC setback functions make it weirder since there would be two thermostat functionalities in the mix.
    The electronic aquastat that come on cast boilers also use this simplified ODR function as and watch the temperature rise. Hydrolevel 3200 series for example
    The more complex tekmar controls tend to overwhelm installers and users. You really need to take their training class to fully understand how to pipe, apply and configure them.
    We would spend hours and hours on the tech support lines talking installers through the installation and settings menu with the complex solar controls we sold. Finally removed them from the catalog.
    Plumbers and fitters are not always well versed on control wiring, logic and settings.
    The same happens with complex mod con boiler setting. My bet is 90% are on the factory default settings, and no ODR connected.
    It a good move that many of the mod con brands offer the basic control version, and the higher option version.
    GGross
    People so rarely go back to the basics: What are the input states? what are my available input parameters? What is my desired output? What equipment do I have and how can I control it with what I can easily know
    And the KISS
    109A_5 Posts: 4,790
    edited November 2
    I don't like Exclusive Maybe type logic. In this case IMO the Tekmar 256 does not do a good job of the intent of the product an how to properly implement it. The Tekmar 253 manual seems to have more and/or different information. But otherwise seems the same as the 256 as much as I looked at it. Maybe the target boiler is not a Cast Iron unit where the T-T controls everything, Maybe the target boiler is a condensing boiler that does not have its own ODR.
    Who knows and they don't seem to be telling.