The circulator on my Superior brand boiler is hot but the pipes are cold - would giving the circ a gentle tap help?
The circs get stuck when immobile and a tap will free them but so far hasn’t worked.
  • Ironman
    Ironman Posts: 7,979
    It appears that you’ve answered your own question.
    Are you sure the circulator is the problem? The system could be air bound.
    Bob Boan
  • rick in Alaska
    rick in Alaska Posts: 1,533
    Also make sure your water pressure is up.
    The pump needs a few psi, or it won't move anything.
    Rick
    EBEBRATT-Ed Posts: 21,379
    You need to Carefully check for power to the motor IF YOU are comfortable doing this and see if the motor is spinning. If the motor is hot and the pipes are cold that means you have (or had) power
  • Dave Carpentier
    Dave Carpentier Posts: 710
    edited October 24
    If the windings are powered up but the impeller isnt spinning, how would you know ?
    Seems a clue that a "tap" used to get them working again.
    My Grundfos have a bleed screw where you can see the rotor spinning. Not sure what brand circ OP has ?
    hot_rod Posts: 28,799
    If it is pumping properly the housing will be a bit warmer than the fluid.
    If it is stuck it will get very hot to touch.
    In some cases it will boil the fluid in the volute if there is no fluid movement
    An amprobe on the wires will show if it is drawing amps unless it is hot and off on overload