No heat/hot water on new install by others
Taco 506 circ zone board- found system wiring like this on arrival. The thermostat terminals have no voltage on board but have 24 v on end switch. The indirect aquastat wiring also seems incorrect but wanted to get some insight from more experienced technicians. When adding 24v from separate source to t stat terminals it activates the circs/zones. (Indirect on zone 6)
Photos for reference.
Comments
-
Just to clarify are you using zone valves?
0 -
he has circulators
0 -
no zones turn on at all?
Have to checked the Fuse on the Relay Box?
Is the In-Direct wired to the Taco Relay or the hyrdostat? Because wiring would be different for both
0 -
fuses all fine, indirect control wired to zone 6 on board, I included pictures in post as well. They used a jumper wire on the indirect control instead of a dedicated 24v which is not an option in the manual
0 -
also no idea why they wired the white wire to the C terminal on all heat zones
0 -
Can you make a circuit diagram of how it is wired now?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements