No heat/hot water on new install by others
Taco 506 circ zone board- found system wiring like this on arrival. The thermostat terminals have no voltage on board but have 24 v on end switch. The indirect aquastat wiring also seems incorrect but wanted to get some insight from more experienced technicians. When adding 24v from separate source to t stat terminals it activates the circs/zones. (Indirect on zone 6)
Photos for reference.
  • pedmec
    pedmec Posts: 1,488
    Just to clarify are you using zone valves?
  • he has circulators
  • tcassano87
    tcassano87 Posts: 154
    no zones turn on at all?
    Have to checked the Fuse on the Relay Box?
    Is the In-Direct wired to the Taco Relay or the hyrdostat? Because wiring would be different for both
  • fuses all fine, indirect control wired to zone 6 on board, I included pictures in post as well. They used a jumper wire on the indirect control instead of a dedicated 24v which is not an option in the manual
  • also no idea why they wired the white wire to the C terminal on all heat zones
    Jamie Hall Posts: 27,894
    Can you make a circuit diagram of how it is wired now?