Does this CGi gas boiler direct vent setup require double wall pipe or not?

Options
image.png

I've contracted to have the masonry chimney demoed and replaced with the snorkel direct vent, but they claim it doesn't need to be double walled. It seems like a liability to me to have a unprotected fully hot vent at ground level!

This is from the manual, page 15. https://www.weil-mclain.com/wp-content/uploads/CGi-S4-Boiler-Manual-0124.pdf

Obtain vent system components

  1. The following special gas vent systems comply with UL-1738
    and ULC-S636 standards and are certified by CSA as the only
    systems suitable for use with CGi boilers (all 3” diameter):
    • Heat-Fab, Inc. Saf-T Vent®
    • Flex-L International, Inc. StaR-34
    • Z-Flex®, Inc. Z-Vent II
    • ProTech Systems FasNSeal

Can/should/must I require they use double walled pipe?

Previous discussion of options https://forum.heatinghelp.com/discussion/204544/what-to-do-with-this-odd-boiler-vent-setup-redirecting-the-vent-into-the-old-chimney#latest

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,090

    Yes. it has to be 1 of the 4 pipes above

    • Heat-Fab, Inc. Saf-T Vent®
    • Flex-L International, Inc. StaR-34
    • Z-Flex®, Inc. Z-Vent II
    • ProTech Systems FasNSeal

    Listed for the install. Nothing else can be used.

  • hot_rod
    hot_rod Posts: 28,434

    I think you have a class 3 requirement if that is a fan assist boiler.

    So the common double wall B vent cannot be used. Stick with the list.

    Double walled is used when you have reduced clearance requirements

    IMG_1645.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jells
    Jells Posts: 689

    So if they can't use double wall, what do I do to make it safe? I don't have small kids but theoretically it's a burn hazard. Do I need to put chain link fence around this thing??