I've contracted to have the masonry chimney demoed and replaced with the snorkel direct vent, but they claim it doesn't need to be double walled. It seems like a liability to me to have a unprotected fully hot vent at ground level!

This is from the manual, page 15. https://www.weil-mclain.com/wp-content/uploads/CGi-S4-Boiler-Manual-0124.pdf

Obtain vent system components

  1. The following special gas vent systems comply with UL-1738
    and ULC-S636 standards and are certified by CSA as the only
    systems suitable for use with CGi boilers (all 3” diameter):
    • Heat-Fab, Inc. Saf-T Vent®
    • Flex-L International, Inc. StaR-34
    • Z-Flex®, Inc. Z-Vent II
    • ProTech Systems FasNSeal

Can/should/must I require they use double walled pipe?

Previous discussion of options https://forum.heatinghelp.com/discussion/204544/what-to-do-with-this-odd-boiler-vent-setup-redirecting-the-vent-into-the-old-chimney#latest

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    Yes. it has to be 1 of the 4 pipes above

    • Heat-Fab, Inc. Saf-T Vent®
    • Flex-L International, Inc. StaR-34
    • Z-Flex®, Inc. Z-Vent II
    • ProTech Systems FasNSeal

    Listed for the install. Nothing else can be used.

    Mad Dog_2
  • hot_rod
    hot_rod Posts: 28,699

    I think you have a class 3 requirement if that is a fan assist boiler.

    So the common double wall B vent cannot be used. Stick with the list.

    Double walled is used when you have reduced clearance requirements

    IMG_1645.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • Jells
    Jells Posts: 690

    So if they can't use double wall, what do I do to make it safe? I don't have small kids but theoretically it's a burn hazard. Do I need to put chain link fence around this thing??

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,940

    Can you show us a photograph of the location for the expected termination of the vent pipe? Are you sure you need it to be a "Snorkel" configuration?

    The Category III vent is for exhaust temperatures that usually range above 140°F, so that is somewhat of a concern when it comes to actually touching the metal vent pipe while the appliance is operating. I might place a metal cage around the vent pipe, with a clearance of about 3 inches from the pipe, using a material that will not allow fingers to get too close to the hot vent pipe. Placing a chain link fence will do the same thing however you would need to be farther away since a small child can fit their arms thru the fence. I have seen expanded metal mesh that will do what you are suggesting.

    Screenshot 2026-10-10 at 10.48.43 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Mad Dog_2
  • hot_rod
    hot_rod Posts: 28,699

    you can use double wall as long as it is listed for Cat. 3 This is one brand on the Weil list you posted.

    Which may be a nicer look than chain link fence.

    The double wall add some insulation, I don’t think I would run much distance of single wall outside.

    You can download venting manuals, most manufacturers use NFPA code guidelines.

    IMG_1652.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jells
    Jells Posts: 690

    Thanks, that's what I needed to know. I'm going to tell the contractor that I want it double walled.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    These vent systems are specific to that boiler. All you have to do is follow the Weil McLain instructions regarding material and install

  • ratio
    ratio Posts: 4,344

    Sounds like this is a hazard that the mgr's engineers didn't consider (as if such a thing is possible). IIWM, I'd talk to the AHJ & see what they say. It doesn't sound like something that has never happened, I bet the inspector has come across this & seen the solution already.