Need help- hydronic system with cast iron radiators
I am trying to install a hydronic system on a single story 1100 sqft ranch style house. I have a heatmaster MF5000 outside stove and old cast iron radiators of varying sizes that are likely overkill (but what I could find used). I need to install 6 radiators that I would like to have set up on 2 zones or have individual valves on each radiator (preferably). Currently have a single circulator pump mounted on the stove but willing to change that. Thanks
Comments
-
-
is this a job you are going to pipe yourself? Here is an example that includes a backup boiler. One pump and two zone valves is a way to get 2 zones. The red line to the right of the pic is where two zone valves would pipe in.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Don’t let any of the outdoor wood boiler people convince you that you can connect the house system directly to the ODWB. You need to separate the house from the ODWB using a heat exchanger as hot rod has shown.
You will have several long term issues if you try to short cut this, not the least of which will be oxygenated water which will rot the radiators.
Think about it: if houses could run unpressurized systems, then why has this industry been requiring it for well over 100 years?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
That wood boiler can heat a small neighborhood of houses that size. If it were me i would look to selling that thing and using the money to pay for a small gas unit and several years worth of fuel personally. I could take care of my heating bills plus the cost of a DIY boiler for around 6-10 years for just the cost of that boiler and my house is about twice that size in a cold climate, zone 6, just a thought..
0 -
Here is what your piping might look like. Find the plate heat exchangers at most wood boiler suppliers.
If you do tie in a back up boiler,here is a piping that adds a shunt pump that sends a small amout of heat backto the OWF to prevent it from freezing if it is left un-fired.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The outdoor boiler you have is much too large for your home UNLESS you install more hot water storage and do batch burning every few days and use a heat exchanger in the home to push the homes cool water back to the heat exchanger keeping the homes circulation as a closed circuit with a second circulator.
0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 132 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements