What's wrong with this install.
  • I saw this at a customer's place , Bosch 151 combi .
  • Ironman
    Ironman Posts: 7,965
    For starters, The floor loops aren’t connected.
    Bob Boan
    GGrossPC7060HomerJSmith
  • Ironman
    Neither is the vent piping or the wiring.
    Bob Boan
    GGross
    hot_rod Posts: 28,524
    Looks like a combi boiler. With that type of heat exchanger design the installation manual probably shows primary secondary piping is required or at least suggested.
    I'm not sure why you would have a mixing valve, as it is a low temperature friendly boiler.
    The installation manual would shed some light on what is proper piping.
    Ironman
    109A_5 Posts: 4,617
    GGrossIronmanAlan (California Radiant) Forbes
  • I have nothing to with the install, just saw it at a job. As @hot_rod said there is no ps piping and there is is a mixing valve which is completely unnecessary. They have the manual for it, apparently they don't know how to read.
  • Grallert
    Grallert Posts: 1,215
    The red tubing ids confusing to me. Is it o2 barrier tubing? Looks like domestic hot non o2 tubing, but maybe things have changed since i've been installing this kind of stuff.
    So now what?
    Will you suggest to the customer it is mis -piped, possibly other issues?
    mattmia2 Posts: 18,231
    edited September 25
    you cna get red oxygen barrier tubing. That doesn't mean that they did, but it does exist.
    Both Rehau and Mr Pex have red oxygen barrier tube.
    Zurn has a red non barrier tube, the stuff you see at Home Depot, etc. So color doesn't mean much when identifying tube.
    The infloor looks more orange. Watts Radiant pex used to be that color. So is some of the PERT tube.
    It should have info printed on the tube every 12" or so.
    If it is non barrier, a stainless pump and Amtrol Radiant Pro expansion tank give you all non ferrous components, so not a deal breaker.
  • Since it is not in my home, I can't see anything wrong. LOL
    I might drop the homeowner or the builder a note to hold back a substantial $$$ amount to make sure that it works properly. Otherwise you may be paying someone extra top remove what is wrong in favor of what is needed. If the installer needs to get it to work before payment, then let the installer bare the cost of ripping out what is wrong with his work.
    HomerJSmith
    It probably will work as shown. The boiler will need to run 15 degress warmer that the radiant required nsupply temperature for the mix valve to operate properly.
    9 loops is a bit much for a typical 3 Cv mix valve, and not knowing the pressure drop across the boiler? But with enough pump power??
    alternatively you can set up odr and it will just rum off the setpoint of the boiler, assuming the radiant only needs around 3gpm.
  • One of the customers employees is installing it. I highly doubt our will be set up on the boiler, that would require reading the manual.
  • I am not a hvac tech, but I work in the trades, I asked someone who installs mod cons about using the odr curve on one and he had never heard of doing that!
  • It is barrier tubing.
    it is easy enough to install the outdoor sensor and turn it on when someone needs to make it work
  • Intplm.
    Intplm. Posts: 3,156
    edited September 26
    Is it natural gas- or propane-fired? Needs a dirt leg on the gas line. And there is a bushing installed on the elbow. That's a no-no.
    109A_5 Posts: 4,617
    There is a dirt leg on the gas line, look at the shadow on the wall.
    GGross