Hi all,
The dehumidifer in my crawlspace doesn't dehumidify. Honestly, I never ran it enough to know if/when it might've stopped working. In the last 9 years I maybe ran it for a total of 20 hours. Not sure how old it is.
The manual doesn't have troubleshooting for the following scenario:
- Fan runs,
- compressor gets hot to the touch,
- capacitor tests ok (46.3µF) according to its rating,
- coils don't freeze
- unit doesn't trip on thermal overload,
- put a thermometer against the coils, fins, capillary tube, that bulb-looking thing, and nothing reads above/below room temp.
- humidistat turns unit on/off at about the right position on the dial according to a humidity sensor I have.
I assume there is no refrigerant. The blue coil looks sus.
Anything I can try? Is this something any tech would/could service?
EDIT: I just noticed I can probably remove that rating plate. I wonder if there is diagnostic anything behind there. I'll go check that now. Eh, nothing back there except maybe a capacitor for the fan motor
Appreciate any guidance,
David
Comments
-
-
welcome to my collection of 4 dehumidifiers since 2010 from which the refrigerant has escaped.
0 -
is it still under warranty? if it has refrigerant in it and the compressor is actually pumping(though possible for the compressor to run but fail to pump, a fairly uncommon failure mode), you should hear it flowing and you should hear it equalize if you turn it off suddenly after it has been running for a bit(you should hear the liquid being released from the capillary tube from the high side to the low side for maybe 10 seconds to a minute or so after the compressor stops).
0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 130 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements