Dryer vent duct
could you explain more about "reline with a properly sized smooth wall 316Ti or 316L ss liner"?is the liner on the exterior surface of the chimney?
the top of the chimney has a rain cap. the flue way formed by the inner clay liner is pretty small, compared with the size of the chimney.
what do you mean by "within 6 inch of the bottom of the opening through the middle of the chimney"?
I talked with a city employee who confirmed the cleanout is needed for compliance to the current code. All the codes are listed here:
The chimney cleanout is documented in the mechanical code instead of building code or fuel gas code:
801.13 Cleanouts. Factory-built chimneys and vents shall be provided with a cleanout opening or access door at the base of the chimney or vent installed in accordance with the manufacturer’s instructions. Masonry and metal chimneys shall be provided with a cleanout opening having a minimum height of 6 inches (152.4 mm). The upper edge of the opening shall be located not less than 6 inches (152.4 mm) below the lowest chimney inlet opening. The cleanout shall be provided with a tight-fitting, noncombustible cover of a minimum size of 8 inches by 8 inches (203.2 mm by 203.2 mm)
this says the cleanout should be located between 6"+ above the ground, and 6"+ below the thimble? it's a pretty wide range.
your previous quote said this:
"Cleanout openings shall be provided
within 6 inches (152 mm) of the base of each fluewithin every masonry chimney. The upper edge of the cleanout shall be located not less than 6 inches (152 mm) below the lowest chimney inlet opening. The height of the opening shall be not less than 6 inches (152 mm). The cleanout shall be provided with a noncombustible cover."
the flue is the opening in the inside of the chimney so this rule says that the cleanout must be within 6" of the "floor" of the inside of the chimney
@mattmia2 the quoted language is from the Building code. if you click my link, then click "Building code", "chapter 21 Masonry", on page 24 it says -
the other language is found by clicking "Mechanical Code", then "Chapter 8 Chimney and Vents", on page 4 -
"the height of the opening shall be not less than 6 inch" refers to the distance from the ground to the opening.
so I think this sentence stands out: "within 6 inch of the base of each flue"
You seriously need a professional level II inspection. So much going on I can see from here. The terra cotta flue tile is severely eroded and does not extend the requisite 2-4" above the crown. The crown appears to be either a mastic gobbed over the crown or rich Ordinary Portland Cement (OPC) mortar crown wash instead of a cast concrete crown with a 2" overhand that has a reglet but into the overhang forming a drip edge 1.5" from the face of the chimney. The flue has to be accessible- this is entombed by the OPC mortar/ mastic crown mess.
The cleanout is for a masonry chimney. If you install a listed liner, the listing applies. I'm not aware of any mfr. that requires a tee with a cleanout for liquid or gaseous fuels. Wood/ pellet/ coal solid fuels typically DO require a cleanout 6-12" below the breaching or thimble. This provides a convenient point of inspection, a cleanout port, and a trash can to collect solid flue deposits and previous clay flue liner and mortar. Since metallic liners do not slough off and burning liquid or gaseous fuels does not result in significant flue gas deposits requiring intermediate sweeping to keep the flue open, they don't need a cleanout. The IRC Ch. 24 discussing sizing liners by NOT requiring the single broad radius bend at the base of the liner (meaning no tee or cleanout).
I quote the IRC and NFPA 211. If your local code is more restrictive, you follow it.
the photo below shows the neighbor's chimneys. the right one has been updated where a new flue has been added on top so it naturally extended the inner clay above the crown by ~1 ft. The flue way is relined with a stainless steel liner. The flue way is accessible by removing the 4 bolts at the base of the rain cap.
the cleanout door will be most likely required by the inspector. I heard he will not inspect the top or inside of the chimney, but mostly rely on the plumber's signoff on the LAA form.
Someone dropped a ss liner, slipped a section of terra cotta flue tile over it to provide a convenient way to slop some mortar up against it to form some semblance of a crown and provide a base for a traditional tile mounted chimney cap. What I cannot see is the stainless-steel support plate REQUIRED by the UL listing.
The whole thing is a mess but, whatever you want. If Hector, the Inspector requires a cleanout then put one in. However, a tee with a 90-degree snout creates massive flow resistance whereas a broad radius bend does not. The bottom line is, it has to work. If if backdrafts into the CAZ then you're right back to the drawing board.
This door is not water tight. There is no problem for indoor use, but if used outdoor, some rain will enter through the gap. Not a concern?
That will work. I would have picked up a Lyemance cast aluminum door or a Minuteman cast iron door in 8"x12" , which provides much better access. These doors have a screw latch, too. Make sure you caulk it on three sides leaving the bottom edge open for drainage.
As long as the flue has a ss liner the sloppy non-air tight fit is not a problem. If someone wanted to use this in a flue, where it leaked dilution air it could be a problem. No problem for a fireplace's indoor cleanout.Note: always provide a cleanout to a fireplace ash pit. Last week a kid dropped my favorite LED work light down into the pit of despair. I tried fishing it out with a magnet on a rope but no joy. I'm leaving it there for Geraldo to find.
Caulk the three sides a thin fillet of red rtv silicone?
I drilled a hole through the mortar at the base of the chimney, and got a wall thickness of 6 1/2". The brick width is 3 3/8". If it is single brick, the clay liner would be 3" thick, this is not likely. If the wall if double brick, two bricks plus the mortar and the clay liner should be about 8" thick?
how do you know that the back of the masonry didn't blow out where you drilled through? chimneys typically didn't have a liner before the 40's or so. it may have been repaired at the top and have a liner there but not in the rest of it.
so the material to be removed is 8" x8"x7". A 9" masonry blade will only be able to cut to a depth of 3", that is not fully through the first brick yet. After tracing the lines, is the next step to do stitch drills and use rotary hammer with a chisel bit to scoop the first layer of brick out piece by piece?
I have been pushing the work back. Now the inspection has been completed. They didn't look at the chimney.
earlier, I drilled 3 holes to measure the wall thickness (6 3/4"). All are 1/4" through holes, two through mortar and one through a brick. The other side of the wall is inaccessible
How to fill these through holes?
mortar
Combustable material in a chimney?
The flue entrance is 5ft above these holes, so this area is not subject to high temp flue. Or 1/4 aluminum rod
- 87.8K THE MAIN WALL
- 129 Chimneys & Flues
- 123 Geothermal
- 79 Pipe Deterioration
- 396 Solar