Acid Cleaning steam boiler in one pipe system
WE have a couple of 2 -3 million btu steam boilers that need acid cleaning. I am concerned the fumes will go out into the system and out the radiator vents in the living units.
What is the experience of others with this situation. There is no king valve to isolate the boilers from the system.
Comments
-
-
To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
how do you know they need an Acid Cleaning?
0 -
Attached is the SDS.
I am the farthest thing from a chemical expert there is.
But to me these reads like something you wouldn't want to breathe.
0 -
Definitely not..I've used Muriatic acid outdoors to clean rust off of concrete. Your concern is very real. With no King Valves or Isolation valves on the returns, there is no guarantee you can contain and then purge it out. If I were you, I wouldn't do it unless An Engineer and OSHA Competent Person signed off on it. Mad Dog
0 -
how much are you diluting it, that will make a big difference. taping up the vents would keep it out of the building, i'd be concerned about flushing the acid formed from the vapors up in the system out.
what are you trying to accomplish here and could you use something like citric acid that doesn't form vapors
0 -
We've also used it to burn out mineral building on wells. Once again, all outdoors and the ability to flush everything out with copious amounts of water. At the VERY LEAST, building inhabitants could complain of eye, nasal and lung 🫁 irritation. Mad Dog
0 -
I use it in my pool from time to time and yeah....
You don't want to be down wind of that. Even highly diluted those fumes are as welcoming as an outhouse breeze
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The best I can say is that it will work. The building should NOT be occupied when it is in use, and the entire heating system must be thoroughly purged of vapours before the building is reoccupied — and I honestly have absolutely no idea how to do that with a one pipe steam system.
There must be some very very good reason you need to use something like that?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
not just vapors but any moisture in the system when the hydrogen chloride gas contacts it will form a hydrochloric acid solution in that water so you need to flush that water out too(and that acid may have unintended consequences).
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements