10" Flue Pipe- Open Tee- Coal to Gas Boiler
So who would reposition the tee and add a DA draft regulator and who would scrap the whole thing even though the COAF is under 60 ppm, stack temp 400 after 15 minutes cold start up with a draft of -0.004-7, and the spillage at just inside the tee bottom is almost the same as through the breech?
Comments
-
what kind of burner is on the boiler? how is it controlling secondary air and draft?
0 -
-
The chimney should be relined with ss sized to the application with the liner brought into the CAZ. That eliminates the need for a cleanout. Yours is way too low to meet code. The connector cannot be cemented into the masonry. Re-pipe it with a bullhead tee, x2 baro damper w/ spill switch wired to the burner. To get the proper gauge pipe, just use 24 ga. ss for a permanent vent connector unless you want to get 22 ga. black stovepipe.
Your combustion analysis numbers were incomplete. Mainly, what was the O2? That is no draft- you need a minimum of -0.02wci for proper burning but not over -0.04. The baro would take care of that. Where did you take your draft reading- btw the boiler and the horizontal draft hood or btw the opening and the chimney? Big difference.
Take the NCI course.
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements