10" Flue Pipe- Open Tee- Coal to Gas Boiler
So who would reposition the tee and add a DA draft regulator and who would scrap the whole thing even though the COAF is under 60 ppm, stack temp 400 after 15 minutes cold start up with a draft of -0.004-7, and the spillage at just inside the tee bottom is almost the same as through the breech?
Comments
-
what kind of burner is on the boiler? how is it controlling secondary air and draft?
0 -
-
The chimney should be relined with ss sized to the application with the liner brought into the CAZ. That eliminates the need for a cleanout. Yours is way too low to meet code. The connector cannot be cemented into the masonry. Re-pipe it with a bullhead tee, x2 baro damper w/ spill switch wired to the burner. To get the proper gauge pipe, just use 24 ga. ss for a permanent vent connector unless you want to get 22 ga. black stovepipe.
Your combustion analysis numbers were incomplete. Mainly, what was the O2? That is no draft- you need a minimum of -0.02wci for proper burning but not over -0.04. The baro would take care of that. Where did you take your draft reading- btw the boiler and the horizontal draft hood or btw the opening and the chimney? Big difference.
Take the NCI course.
0 -
If it were me, I would install a pair of auger fed EFM DF520 coal stoker boilers to tie into this original coal fired beautiful gravity hot water system and leave the chimney as is, but that is just me.
EFM also has dual fuel DF520 coal stokers that operate on gas or oil
The EFM DF520 has an 8 inch flue with a 3 inch steam chest tapping and two 2 inch return tapping's.
You may be able to get by with one EFM DF520 and a gas burner as they are pressure tested and welded for steam service right out of the welding shop in Emmaus, PA.
1 -
Your crazy my dude! This was a cold start up and simple CO/draft check. Draft was taken at the breech and just inside the open tee. Been that way for 80 years. This boiler is going to be turned into a permanent basement museum piece because the piping is rotted around it.
0 -
What are you replacing it with?
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements