Ultra 155 E02 Low Spark
I have a Weil Mclain Ultra 155 series 1 which keeps throwing an E02 code. I went through and did a boiler maintenance, cleaned the heat exchanger, cleaned the combustion chamber, replaced the igniter. Unit worked great for a couple days but the error came back. Noticed that the spark seemed "low". Meaning you could barely hear it. Checked the Ignition cable and it was on the low side at 955 Ohms. Replaced that but still no change. The spark seems very week. Any ideas where to go next.
Comments
-
does it work sometimes?
if it does I would look at a few things. first the easiest, check static and dynamic gas pressures are in range for your fuel type when the unit is off, and at high fire.
next I would check to make sure your flue pipe doesn't have a belly forming, holding back condensate and creating a restriction in the flue (check both vent pipes for any blockage)
clean the condensate trap
955 is within tolerance according to the WM manual so that cable was never an issue.
what were your steps for " a boiler maintenance, cleaned the heat exchanger, cleaned the combustion chamber" to me these three things are all the same task, just stated 3 different ways. can you elaborate what you did? and do you have photos of the finished cleaning on the fire side of the heat exchanger? did you get anything like coffee grounds to flush out of the drain?
any other odd things with the unit? harmonic sounds from the flue pipes? weird noises etc
2 -
i followed the manual for boiler maintenance using the flat bar cleaning between the heat exchanger, vacuumed out all the debris, checked the condensate trap, replaced igniter and seals and cleaned the combustion chamber. dont believe i missed anything.
yeah i didnt think it was the cable but since the unit is 17 years old and it was on the low side of the tolerance i was hoping that would be it.
The only odd noise is the lack of noise from the igniter. it used to snap or crackle during ignition. Now its almost silent like there is no spark.
I did check the low voltage terminal 9 to ground and it was only 2.2v during ignition. checked ground to X1-6 which was good. Unfortunately, this path leads me to a new control module.
0 -
Series 1 Ultra? Original block?
Get your analyzer out, bump start it, and tune it.
Natural or LP? Do you know the pressure drop across the gas valve during TFI?
0 -
There may be multiple issues. Low flame signal and the weak spark. Although I believe flame signal is only valid when there is a flame present " only 2.2v during ignition "
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements