LG Therma V 9kW – DHW Loop Not Triggering

Options
Willits
Willits Member Posts: 6

Hello All,

I have a 9kW LG Therma V monobloc heat pump installed two years ago. I’ve hit aan issue where the unit has stopped engaging the DHW cycle, eventually falling back to the immersion heater after the programmed 30-minute delay.

The Symptoms:

  • Space Cooling/Heating: Works perfectly.
  • Cooling/Heating on - DHW call: When a DHW cycle is called, the outdoor unit remains in heating/cooling mode. The controller displays “Outdoor unit operation” and “Water pump operation.”
  • Fallback: After the 30-minute delay, the internal immersion heater kicks in. The display then changes to “DHW heater operation” and “Water pump operation.”
  • Cooling/Heating off - DHW call: When a DHW cycle is called, the outdoor unit remains idle. The controller displays “There is no monitoring information” for the first 30 minutes.
  • Fallback: After the 30-minute delay, the internal immersion heater kicks in. The display then changes to “DHW heater operation”.

Operation:

  • No Error Codes
  • 3-Way Valve: Visually confirmed to be operating.
  • DHW Tank Sensor: Correctly reporting tank temperature (39°C - 42°C), so the sensor appears functional.
  • Flow rate: set to optimal and running between 11 and 31 lpm as needed.

I understand the only sensor for the DHW is the tank sensor. I am going to order a replacement, but it does seem odd that it reports the tank temperature but the unit does not see the input to trigger the DHW loop.

In the pics I just switched off from cooling mode, so the feed and return temps are residual from that. After a while the feed and return temps become equal.

Any advice is appreciated.

Thanks, Peter

IMG_20260420_115607082_HDR.jpg IMG_20260420_125556243_HDR.jpg Withour DHW.jpg With DHW after 30 minutes.jpg

Comments

  • hot_rod
    hot_rod Member Posts: 27,519

    the diverting turns, the pump is running? Could be an air lock in the piping between HP and tank

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Willits
    Willits Member Posts: 6

    The diverter doesn't get the signal from the HP to switch to the DHW circuit. I tried switching over manually to make sure there was flow and its good for both the heating/cooling and DHW circuit.