Gas boiler multizone apartment systems need heat turned off, hot water kept on
4343 Member Posts: 3
edited April 11 in Gas Heating
Gas boiler multizone apartment systems need to have the heat turned off for the summer, while keeping the hot water supply on. Some boilers are very old, from 1971 HB Smith brand, others are a few years old McLeins. Most of them have the high and low aquastats.
Thank you
  • pedmec
    pedmec Member Posts: 1,361
    You need a boiler management control system. Tekmar and Heattimer are just 2 that come to mind off the top of my heat. There are tons of these available.
    EBEBRATT-Ed Member Posts: 20,217
    If you producing domestic HW from the boiler system your boilers should be all set up for this. With your thermostats turned down you should get no heat but should get domestic HW.
    If it doesn't operate correctly you could have a bad zone valve a bad flow check valve and the aqustat settings could be out of adjustment.
    EdTheHeaterMan Member Posts: 12,247
    edited April 11
    The information given so far is insufficient to answer the question asked.
    1. We know this
      1. there is more than one boiler
      2. some are HB Smith that are old from 1971
      3. some of them are Weil McLain that are newer
      4. these boilers produce space heating and domestic hot water
      5. most of the boilers have 2 aquastats.
    2. We don't know this
      1. how many boilers there are
      2. if the boilers are in the same building or if the boilers are in separate buildings: like one boiler per building.
      3. what size boilers they are
      4. are the boilers manifolded together as one large system or if there are separate systems
      5. how the boilers make hot water
        1. indirect tanks
        2. heat exchanger coils with storage tank(s)
        3. tankless coils inside the boilers
        4. or some other potable hot water source that is heated by the boiler(s)
      6. what existing controls are on the boilers
      7. what controls the hot water temperature
      8. what controls the room temperatures in the apartments
      9. if there is even a problem with apartments over heating in the summer as a result of the hot water operation
    But without that additional information, we can all answer this with the experience we have all had on similar buildings. I remember shutting down a 220,000 BTU boiler for the winter that was only used to generate heat that goes into a shell and tube heat exchanger that fed a 2000 gallon domestic hot water tank that was covered with 3 inches of asbestos insulation with a plaster coating that was in pristine condition. the reason for shutting the boiler off for the winter was that no one lived in the building in the winter and the entire building was drained of water to prevent freezing water damage.
    But that info won't help in this case.
    EDIT:
    The more info we have, the lower the cost of the solution to the problem: For example @pedmec solution is a complete control system for thousands of dollars. @EBEBRATT-Ed solution is to repair something that is already there. That has to be less expensive.
    And since some of those boilers are from 1971, I believe that this situation has come up at least 54 times over the last half century. But that is just a guess
  • pedmec
    I was under the impression he was looking for something new to upgrade the old.
    edited April 11
    I thought he has 5 boilers in one building. but the more I thought about it, I believe there are many buildings with individual boilers in each building. Why would you have several boilers manifolded together and have 1971 boilers in the same system as boilers that are only a few years old? Makes no sense. that is when I thought of separate buildings. BUT… I am only guessing like you.
    @4343 needs to offer more details.
    I wonder if that is a new member that replaces @4321 from the other building down the parking lot of the apartment "systems" 🤣
  • 4343
    I just found all these comments in the blog, had no clue they were in here. Sorry, I just signed up, and I'm still learning my way with the website. To clarify, there are total of 20 buildings in the development, built in the late 1940's.. Some buildings have 15 apts, others 20-25 apts. serviced by a single boiler. They all have radiators, mostly still the original plumbing, the boilers provide heat and hot water.
    My question is, with the warm wether around the corner and ni need for heating how do I set up the boilers so they still supply hot water, and the heat is off
  • 4343
    Every boiler room has a heat exchanger for making hot water. The heat for the apts. is controlled by the boiler settings. There are no individual radiator controllers, very outdated setup
    @4343
    If it has been installed for years it probably already does what you want it to do. You will find a aquastat (hot water control) that probably senses the boiler water temperature.
    It could be set at a temperature from about 140-180 deg 160-180 is probably the most common. This control is referred to as a low-limit and maintains the boiler at the minimum temp required to provide domestic hot water 24/7.
    How your heating system is controlled is another matter. You could have thermostats in every apartment to control zone valve and or circulators or it could be all one zone based on outdoor air reset.
    The wiring for the heat and the wiring for the DHW come together usually to start the boiler. When the heating system is not calling for heat it should still work for DHW.
    You may not have the most efficient system but that is the way it was done.
  • pedmec
    You still need to provide more info. Are you saying the boilers are supplying hot water thru a tankless coil, indirect fired hot water heater. or storage tank? maybe even a sidearm instantaneous? You state one boiler per building if i am reading right? You dont say the type of water heater.
    All the old buildings that i take care of use a outdoor temperature control (Honeywell T678 or similar) that turns the circulator on. This is the rudimentary way of suppling heat to the tenants prior to the advent of logic control. Boiler stays on year round so the hot water, if boiler is being used to provide the hot water, is always available. A flocheck valve or valves depending on piping prevent gravity flow during the no heat demands. This is the basic setup for older buildings that haven't
