Quieter zone valves than Taco Zone Sentry
I currently have zone sentry Z075P2–2 two way valves installed.  My house is very open and quiet. When these valves open or close, the winding noise is loud.
Can any quieter actuators be installed on these bodies or would a new valve be required all together?  Are the Taco 571 valves much quieter? Any other suggestions?
    hot_rod Posts: 28,343
    Thermal actuator type valves will be silent. Any motorized or spring return type ZV will make some noise.
    Most all of the newer designed thermal actuators are low current draw type, 250 mA, 3W holding current.
    Here is an option. It has a unique Twistop actuator for manual opening and green indicator when open. Various connection types and sizes available.
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/656354 - Product Overview - Caleffi.pdf
  • Thanks Bob. That does look good. It looks like the three-quarter inch 656314 would work well in my case.  Any problem with mounting it such that the actuator is horizontal? That would fit in the spaces I have.
    Any position for mounting. Try to avoid the actuator hanging below, in case of a leak it would run into the electrics. You can run 7 or so of these on a 40Va transformer.
  • That should work, thanks, Bob. I think I’ll try one and just make sure it all works out and then do the rest of them.
  • Are you sure you have the newer actuator? They're pretty quiet.
    rick in Alaska
  • It has a date code of June 20 20 it looks like. 06/20.
  • Looks like your picture, too, I should have said.
  • OK, then. You've got the updated actuator.
    Among zone valves, Taco's are the loudest of this design.
  • I guess I’m going to try a thermal actuator then and make sure that works OK. The taco works great, it’s just a noise.
  • I have 13 taco zone sentry valves installed in my home, and they are very quiet. I know I might sound biased, but really don't think they are noisy at all. Taco does offer the 571 valve heat motor design which is virtually silent. you can certainly try them. they are very robust, and will las for many quiet years:)
    Joe Mattiello
    Taco Comfort Solutions
    Alan (California Radiant) Forbesrick in Alaska
  • jeff4444
    jeff4444 Posts: 40
    edited October 2023
    thanks. Every time they open here, in the basement, you hear the winding sound on floor 1. Unfortunately 2 were installed in a bedroom closet and this is the bigger problem. Two zones opening and closing will drive a light sleeper somewhat crazy! :)
  • I am considering the 571 as well, thanks. The install doc says they should only be mounted vertically however which might be a space problem. Existing ones are mounted horizontally and that would be the better replacement plan.
    It comes down to how much you like a silent home :)
    My 70 year old ears can barely hear that valve closing on my shop bench. Others with better or normal :) hearing could probably hear it across the room. If the piping touches any framing or sheetrock, that seems to magnify / transmit the noise
    Thermal actuators are used on radiant manifolds, sometimes mounted in closets next to a sleeping area, and they are completely quiet.
    The Belimo ball type zone valve is very quiet. I just compared both.
  • would be really nice if there was a quiet actuator I could install on the existing, and plumbed, taco valves.
    hot_rod
  • @hot_rod How does Belimo compare to Caleffi soundwise?
    I credit Belimo with giving you a lot of data on their components. I also applaud SupplyHouse for adding that tech and submittal info on most of the products they sell.
    In this case they show the noise level of that Belimo actuator.
    35 dB That is about the level of a persons whisper.
    Personally I cannot hear it open a close at all. But I am in the hearing aid years now :)
    I have a decibel ap on my phone, I could record both. I think the Taco Sentry is still a spring return, hence the fast close. When you wind a gear train fast, a 7 sec close, that is where you hear spring return valves.
    I thought Taco mentioned slowing down that close off, that would reduce noise I suspect.
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Belimo-Z2075Q-K-CQKB24-RR-Submittal-Sheet.pdf
  • jeff4444
    jeff4444 Posts: 40
    edited March 26
    Just to wrap this up, I did install the valves that hot rod recommended. It totally solved my noise problem, they are silent and have been running now for a few years with no problems. Thank you, Bob very much!
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/656354%20-%20Product%20Overview%20-%20Caleffi.pdf
    Alan (California Radiant) Forbesmattmia2PeteA
    mattmia2 Posts: 18,101
    reading through this, maybe in hindsight you could have just got a piece of large, thick foam pipe insulation and slipped it over the valve.
  • jeff4444
    jeff4444 Posts: 40
    edited March 26
    why do you say that? These two valves were in the closet of a bedroom. The house is very quiet at night. These wind up a mechanical gear and it makes a worming noise as it springs closed I guess.
    I tried to put Styrofoam board around it, but no good, it is an obnoxious sound.
    In fact, I can hear one of these valves that’s in the basement from the second floor of the house.
    If noise is going to be an issue, the valves hot rod suggested are silent and I don’t imagine they cost much more than the taco costs.
    I don’t remember the exact cost, but I bought them from supply house and I wasn’t shocked at the cost! I soldered them in and problem solved.
    a valve with any type if actuator will have a maximum ambient temperate. If you insulate over an actuator they may may over heat
    GGross