Seeking advice, new to boilers, boiler broke over winter
triode
triode Member Posts: 5
edited March 24 in Radiant Heating
Recently purchased a home (have not yet moved in). It has a 52 year old Burnham Series 4, 200,000 BTU boiler. It was steam, and someone (long ago) converted it to water. It was working when we purchased the house, but inspector said "its old, replace it". I called a few people who really wanted to push me to replace it outright, but were quoting me crazy money quotes to replace it.
Just for notes, it is a two story house, four radiators upstairs, six radiators downstairs, boiler in the basement. It used to vent out the chimney, but that failed and they are now venting with a blower out the basement window.
Long story short, I have had two boiler techs come by and say things like "well, the cast iron boiler itself looks ok, but a lot of these other things were not maintained" or "gee the boiler can't be 52 years old, it looks good, maybe just clean it and let it run". Shortly after this, the gas valve failed, during some of our coldest times, so I drained the boiler as much as I could (boiler drain was locked up, in fact the water feed valve and auto-fill and bypass valves were locked up).
Here is the situation now: boiler mostly drained. Gas valve is bad. I was going to replace the valve with a universal pilot ignition (Honeywell Y8610U-6006/U). I would also need (I am pretty sure) to replace the autofill and back flow preventer (BFP), as well as the bypass valve and main inlet valve. There is a Aquastat on the side of the boiler, no idea if it works. The boiler pressure/temp gauge is also stuck as it did not move from 10psi after I opened the boiler and drained 80 gallons of water out of it, so that would need to be changed. The burners need a really good cleaning, and the manual gas valve is probably 100 years old (would change that too). Would probably add a rollout switch as it (from visual burn marks) had an issue with that in the past due to a broken chimney.
I know none of you can see it, but the boiler outside is in rough shape. Figure it would be approaching $1000 in parts to do what I mentioned above, and although I am handy and an engineer and have done a lot of electrical, I have never done boilers. Should I try to get this Burnham going? The three local heating / boiler places I called for quotes on a replacement boiler want outrageous money. They are asking what is essentially surgeon prices to yank and replace a boiler.
I am attaching a drawing of what I think is the current setup. I am not sure if I would need to change the B&G components: SA 1&1/2, 1AF-1&1/4, ATF12, but I have no idea how to test them. The system was "working" before the valve failure, in that it heated the home nicely, but not sure if it was "correct".
Again, do I spent $1,000, change the valves, auto fill, BFP and gas valve and fill it (would have to read about filling it) and hope for the best, or just call someone and say "take all of my money and then some" and have it replaced?
    ethicalpaul Member Posts: 8,773
    edited March 24
    Welcome to NJ! (just guessing)
    Show us some pictures. We like pictures!
    Based on what you said, and your description of yourself, I would spend the spring learning about cast iron hot water boilers and their controls and get it going.
    You will be able to use this knowledge for the next X years living with this boiler (or its eventual replacement), and you can always spend the big money later if you don't like the results of fixing up this old one. Or you can do like I (and several others) did and install your own replacement boiler.
    PS: free hint: your expansion tank in your drawing looks like the old kind that they strapped up to the floor joists that is just a tank with no bladder. Which is fine, but it's probably flooded so drain it. You can't tell by tapping if it's full of water.
  • triode
    edited March 24
    Hello,
    The house is located in the midwest, actually.
    Will grab some pictures next time, all of the pictures I have are just of nameplates.
    Yes, the expansion tank is strapped up to the floor joists. It has 18 Gallons, 75lbs working pressure and D-1/86 written on it. I am guessing the drain on it is locked up. It is always amazing to me that most people never exercise a water valve and expect it to work years later. I am still confused about how this tank with no bladder operates (e.g. how does it not fill when you fill the boiler? You must have to shut it off somehow during the fill cycle, or is that what the B&G ATF12 does? It must be, right, otherwise the autofill valve would fill it, or are we just relying on compressed air in the tank for this?)
    edited March 24
    The air inside it has nowhere to go (that's why they put it in the ceiling), so it compresses to equal the pressure of the water in the system.
    But after some years, all the air either leaks out or it gets absorbed into the water and so these old tanks are often waterlogged and then they don't provide any compression (because you can't squeeze water very easily)
    But anyway, you will learn all kinds of other helpful nuggets of knowledge as you get your boiler operating again and you will not be subject to the whims of market pricing of scarce knowledgeable contractors anymore.
    (the expansion tank example is an interesting one—I helped a friend drain hers which solved her leaking pressure relief valve issues after 3 different contractors were there and couldn't figure it out. Then 6 months later she had another plumber there and he was even old like me and told her "there are no expansion tanks that don't have bladders". You can't make this stuff up!!! She now knows more about her boiler than at least 4 different HVAC Plumber guys in her town! This is not a statement on her or my level of awesomeness, but rather a statement on how hard it can be to find knowledgeable contractors especially when it comes to older systems. But if you use the Find A Contractor feature on this site you will increase your odds significantly)
    GGross
  • Grallert
    Grallert Member Posts: 1,116
    "just relying on compressed air in the tank for this". You got it. That's how it works.
    hot_rod Member Posts: 27,442
    Did any of the contractors perform a heat load calc? How many sq ft of home? A 200,000 boiler is quite large.
    It is always a tough question when to start new or keep dumping $$ into old boilers and components.
    You could do a heat load to at least get a starting point for the project.
    How do you generate DHW?
  • triode
    Funny, before I even knew anything about boilers, I know from my other work that when you put in an HVAC, you need to know the load. I asked them, and every contractor had some magic formula.
    HVAC guy #1: 200,000 is very large, but just looking at your home i can tell you 150,000 is fine.
    HVAC guy #2: The person who speced out this burnham must have know what they were doing.
    HVAC guy #3: 200,000?!? Well, it is a large old house, I guess we should put that back in.
    The house is about 2200 sq feet. It is drafty. I actually tried a load page I found, but it started going down roads I did not have measurements for (how long is each wall on each side, etc). The ceilings are 10feet high, walls are plaster, ceilings are plaster, windows need work and I am sure leak a lot.
    There is no substitute for a load cals. Room by room is ideal to confirm all the emitters match the actual room loads.
    Just a WAG with a fairly big load number of 30 btu/sq ft.
    30 btu/ft. X 2200= 66,000 btu/hr required.
    Your current boiler/ bid, 200,000 boiler at 85%=170,000 output.
    How do you feel about these guesstimates?
    As you plan on updating the building envelop , the load should continue to go down. As well as fuel use :)
    A modulating type boiler is ideal for several reasons;
    Efficiency, with outdoor reset, temperature always modulates
    Comfort afforded by continuous circ via ODR
    Boiler can derate as you continue to upgrade building, if you need 66K now maybe that load drops to 40K after upgrades.
    A % of the year you will run in 90% + condensing mode
    Combustion air grills can be eliminated
    Rebates available in many areas for efficiency upgrades www.dsireusa.org for info on that
    Grallert
  • triode
    edited March 24
    Just to note, I am watching this video: https://heatinghelp.com/systems-help-center/classic-hydronics-seminar/ and at about the 1 hour and 17 min mark, he is talking about a small residential boiler with the circulation pump at the intake of the boiler at the feed line. This is very similar to my setup (which was, at least before the gas valve failure, working). Should I consider moving it? I have read posts before that it should be moved. That pump is on some old large iron steam pipe. I am guessing it would not be fun to move it, particularly because the return lines are much smaller than the outlet lines.
    I will note that my feed line is after the circulation pump though, just like I drew it.
    mattmia2 Member Posts: 16,722
    please edit to remove prices, we can't talk about prices of services. i will say if you're replacing the boiler you replace all of the trim and all of that and the fittings and wiring to connect it all up adds up pretty fast, even the big pipe fittings to connect it to the mains are pricey although if you do the load calculations you might find that you can adapt that down and use much smaller piping around the boiler.
    are you sure this started out as steam and not gravity hot water?
    if it is indeed a gravity hot water system a conventional boiler needs protection from the low water return temps, a modulating condensing boiler gets more efficient with the low water temps.
    i would not change it to pumping away until you replace the boiler.
    replacing the gas train with a modern combination valve would not be a difficult job for a competent tech however you do need combustion analysis equipment and know how to use it.
  • PC7060
    PC7060 Member Posts: 1,800
    "Just for notes, it is a two story house, four radiators upstairs, six radiators downstairs, boiler in the basement. It used to vent out the chimney, but that failed and they are now venting with a blower out the basement window"
    Did the occupants survive?
    Unless you are rebuilding chimney you are looking at a MODCON or a power vent boiler
  • triode
    mattmia2 said: "are you sure this started out as steam and not gravity hot water?" Absolutely. It had the glass sight next to it and a sticker on the boiler pointing to "lowest water level permissible". The top hole for the glass sight now has a gauge and the bottom has a plug.
    PC7060 said: "Unless you are rebuilding chimney you are looking at a MODCON or a power vent boiler", the occupants survived, it was just the boiler front panel that was burnt. The unit now has a power vent (not sure what you call it, a blower motor hooked up to a vent that vents the top of the unit to the outside), but I am literally looking at rebuilding the top of the chimney and putting in a steel liner so I can just draft vent it.
    Keep in mind, I don't know what I am doing yet.
    What does a radiator look like? Someone could have accidentally ordered a boiler with steam trim and swapped the trim. Is the inside of the sight glass crusty? If the boiler is only 50 years old, compression tanks were kind of on their final days at that point, it would be weird if someone converted the boiler in the 80;s and added a compression tank instead of a bladder type tank unless @DanHolohan was their B&G rep.
    4GenPlumber
  • 4GenPlumber
    4GenPlumber Member Posts: 162
    What year was the house built? Sounds like the boiler was when they sold the same block for either steam or hot water.
    109A_5 Member Posts: 3,976
    There are pros and cons either way. Your boiler (the block) could fail in 6 months or 20 years. The old stuff is relatively simple.
    High tech stuff can fail too and gives Techs more grief to restore operation, and they need more annual maintenance just to keep them working.
    How did you determine the gas valve is defective ?