Thinking about purchasing this for sub 1300sf slab on grade home. Anyone have experience with this make?
Comments
-
Hello and welcome. I don’t have any experience with that brand. I’m sure it will operate fine when installed correctly with proper attention to air ducting and etc…
Depending on location and budget however I would reconsider your approach for that type of home. If you haven’t already poured you slab, I would suggest radiant hot water, ductless split heat pumps for your ac/shoulder season heating. Good luck!
THINK
0 -
That would have been my preference but there’s already 648 sf of concrete already as it was an existing apartment…
0 -
it never hurts to do a heat and cooling load calc. New tight homes can be in the teens for btu/ sq ft in the heating side
15 btu/ ft X 1300 sq ft is around a 20,000 btu/ hr load
Oversized equipment is one of the most common issues we see at HH.
Even worse on the cooling side where it may not run long enough to dehumidify. A cold, clammy home is no fun 🫣
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
500 Sq Ft per ton is old old school
a proper manual J room heat load loss must be done.
Then you need a manual D Duct design0 -
Much too large for the space, but the free gift is enticing.
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements