Recommendations
Thinking about purchasing this for sub 1300sf slab on grade home. Anyone have experience with this make?
  • AndythePlumber
    AndythePlumber Member Posts: 106
    Hello and welcome. I don’t have any experience with that brand. I’m sure it will operate fine when installed correctly with proper attention to air ducting and etc…
    Depending on location and budget however I would reconsider your approach for that type of home. If you haven’t already poured you slab, I would suggest radiant hot water, ductless split heat pumps for your ac/shoulder season heating. Good luck!
    THINK
  • rickster26
    rickster26 Member Posts: 2
    That would have been my preference but there’s already 648 sf of concrete already as it was an existing apartment…
    hot_rod Member Posts: 27,445
    it never hurts to do a heat and cooling load calc. New tight homes can be in the teens for btu/ sq ft in the heating side
    15 btu/ ft X 1300 sq ft is around a 20,000 btu/ hr load
    Oversized equipment is one of the most common issues we see at HH.
    Even worse on the cooling side where it may not run long enough to dehumidify. A cold, clammy home is no fun 🫣
    pecmsg Member Posts: 7,053
    edited March 22
    500 Sq Ft per ton is old old school
    a proper manual J room heat load loss must be done.
    Then you need a manual D Duct design
    HVACNUT Member Posts: 7,434
    Much too large for the space, but the free gift is enticing.