Changing Beckett AC relay and a new transformer
kmag320
kmag320 Member Posts: 3
The Beckett AC relay has been making a funny noise while it's running the oil burner. The burner will cycle on and off frequently even when the room is way below the set temperature. If I tap on the relay it will turn the burner back on, so it really seems like I need to replace the relay. I ordered the Beckett 51950U AC ready kit. I see it comes with a 40v transformer. The transformer I currently have on the burner is 24v connected to a Beckett Genisys 7505 control.
Should I put the new 40v one on the burner or just stick with the old 24v? Can I cause any problems going up to the 40v? If it matters, I also have a very old round Thermo pride thermostat.
    Jamie Hall Member Posts: 27,697
    Are you quite sure that that transformer is 40 Volts (40 V) —or it it 40 Volt Amperes (40 VA)? That is not a trivial difference! If it's 40 Volts and you swap it ono the existing burner controls, you'll likely fry everything.
    mattmia2 Member Posts: 17,902
    (i'm assuming it is 40va since 40va is the common size of 24vac hvac xfrmr.)
  • kmag320
    I got a better look at the old and new one and it turns out they are the same. 40va on the 24vac.
    Then you'll be fine.
  • kmag320
    Does it pay to put a new transformer or just change the relay?
    If the old transformer is the same rating and is putting out 24 volts or so, leave it be. Transformers either work or they don't.
    HVACNUT
  • HydronicMike
    HydronicMike Member Posts: 411
    if you bought the whole kit keep the transformer as a backup. If you didn’t buy the kit, you can replace the ac ready kit relay with either just the relay on the plate, or less expensive a RIB.
    HVACNUT
