Changing Beckett AC relay and a new transformer
The Beckett AC relay has been making a funny noise while it's running the oil burner. The burner will cycle on and off frequently even when the room is way below the set temperature. If I tap on the relay it will turn the burner back on, so it really seems like I need to replace the relay. I ordered the Beckett 51950U AC ready kit. I see it comes with a 40v transformer. The transformer I currently have on the burner is 24v connected to a Beckett Genisys 7505 control.
Should I put the new 40v one on the burner or just stick with the old 24v? Can I cause any problems going up to the 40v? If it matters, I also have a very old round Thermo pride thermostat.
Comments
-
Are you quite sure that that transformer is 40 Volts (40 V) —or it it 40 Volt Amperes (40 VA)? That is not a trivial difference! If it's 40 Volts and you swap it ono the existing burner controls, you'll likely fry everything.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
(i'm assuming it is 40va since 40va is the common size of 24vac hvac xfrmr.)
0 -
I got a better look at the old and new one and it turns out they are the same. 40va on the 24vac.
0 -
Then you'll be fine.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Does it pay to put a new transformer or just change the relay?
0 -
If the old transformer is the same rating and is putting out 24 volts or so, leave it be. Transformers either work or they don't.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements