Is 6psi steam with no vents a problem?👀👀
Title is for attraction. I’m quoting a replacement boiler for a public library. At least that’s what they think they need. What they actually need is a venting/trapping plan for the building piping. Built in 1853 and a large addition added sometime in the 1950s. The homestead is now a large public building. Current boiler is an LGB 8 natural, with boiler feed pump, 3 zone valve header. Just obscene water hammer, crazy fuel consumption, eats a boiler every decade and has been since the 1950s. I’ve audited the building and can find no intentional venting of any kind. There are copper fin tube fan coils that have been repaired by brazing ruptures shut. And one active rupture that is acting as a vent currently I suppose.
2 pipe steam with thermostatic traps on all rads/fan coils. The larger zone main supply runs out about 80’ and deadheads a tee and splits to two separate runs on each exterior length of the addition. At the end of main drip connection there is no venting or trapping, simply drops down to a wet return and runs back to the feed reservoir.
The smaller zone is similar except it has a dry return and again no venting or trapping. Just drops to the wet return and back to feed reservoir.
The third zone is pointless, as it simply leaves the header and runs about 30’ to a point where it just tees into the smaller zone’s end of main supply. I have no ideas why this was ever done, but I had to put it out there. There is no radiation off this 3rd zone.
Now, in all these years all our local guys have done is replace boilers and crank the pressuretrol up to 6 psi, changed a rad trap or two along the way. I’m told by the maintenance man who monitors the boiler regularly that it actually build 6psi at times, and in the 8 hours I’ve spent there I’ve seen 3.5 on a mild day.
looking for opinions on venting and trapping. Currently thinking B&J big mouths at end of main and f&T traps to separate the supply from wet. Am I missing something? It seems so silly what I’ve seen so far, but there is always something to learn with steam heat. Thank you in advance fellas
THINK
Mad Dog_2
    Steamhead Member Posts: 18,400
    Oh boy- where to start…………..
    Especially where a return tank and pump is used, you need traps. I'm guessing there is likely a large trap where all the returns go into the boiler-feed pump. That's wrong. You need a trap on each drip so steam will not enter the return lines. These returns are not large enough to handle steam, and often will bang when someone uses a "master trap" at the tank.
    Now….. assuming all these returns slope down to the tank, you can vent the mains through them. You'll need an F&T on each drip, and on longer mains a crossover trap as well to add venting capacity. If you're using an H-pattern F&T such as this Barnes & Jones:
    https://barnesandjones.com/wp-content/uploads/2024/02/Float-Thermostatic-2000-H-Series-125-psig.pdf
    you can use the extra tappings to mount a Big Mouth so it will pass air into the return, which saves some piping work.
    Once everything vents out properly, you can grab the pressuretrol and CRANK IT DOWN!!
    Where is this job located?
    Consulting
    Jamie Hall Member Posts: 27,228
    As above. And in answer to your clickbait header — oh yes indeed it is!
  • AndythePlumber
    AndythePlumber Member Posts: 55
    thanks guys. As always appreciate your input. The job is located in Binghamton NY steamhead. Excellent advice on the h pattern. There is no master trap. Steam regularly dumps out the reservoir overflow. I just couldn’t believe what I was seeing and all the years this has been going on. I suppose it’s a fantastic testament to the amazing resilience of steam heat in general. After all the building does heat. Toasty warm in there.
    Also want to note. After getting a good clean surface at the inlet of the supply header I only ever measured 210f at 2-3 psi. Must be really wet steam? I would expect 220/225 at that pressure. Your thoughts?
    THINK
    109A_5 Member Posts: 3,874
    edited March 1
    Why do they think they need a boiler, what changed ? I don't think you will build much pressure with a rotted out boiler.
    Do you think they would go for the improvements if they think they just need a boiler ?
    With the improvements (actually corrections) I could see less fuel and water consumption, quiet heat and a much greater boiler change out interval.
    Intplm.
    @AndythePlumber said "Steam regularly dumps out the reservoir overflow."
    Now we know why the boilers don't last. With all that steam leaving the system, you need a lot of fresh water coming in to offset the loss. That much fresh water will rot out the boiler quickly.
    Consulting
    EBEBRATT-Ed
  • AndythePlumber
    the boiler sections leak when the boiler cools down. Refractory and debris smothered the flame sensor recently and that when we arrived to help. They will definitely do the corrections along with a the boiler. The library’s director is a sensible man and seems to have a new lease on life having someone who is capable of actual improvements. 😃 I agree. They will have some serious fuel savings, and the water hammer…it’s obnoxious. They have gotten used to it, somehow. I couldn’t believe my eyes and ears
    THINK
    EBEBRATT-Ed Member Posts: 20,079
    Agree with @Steamhead 1000%. Steam out the boiler feed tank vent means a ton of MU water. It will rot the boiler and all the boiler feed piping (maybe the tank and pumps as well) and it will rot a boiler very quickly.
    Intplm.
    edited 2:21AM
    @AndythePlumber , the LGB boiler is not known for its longevity, nor does it have any provision whatsoever for the use of probe-type low-water cutoffs. We all know most folks don't blow down their float-type LWCOs, with sometimes catastrophic results. Look at the Peerless 211A-06, which should last longer if properly taken care of, and where at least the secondary LWCO can be probe-type.
    You could also look at installing several smaller boilers, one for each zone. This would eliminate the zone valves and likely the boiler-feed pump too. Fewer moving parts and redundancy are worth the extra effort.
    Consulting
    Intplm.
  • 4GenPlumber
    4GenPlumber Member Posts: 112
    edited 3:06AM
    I have a customer with a 2 pipe Webster system if I remember correctly. The house has been added onto multiple times. There are F&Ts at the mains and steam traps at built in convectors. The only vent on the system is the wide open vent on the condensate pump. Recently moved the pump for another addition where they dug out a deeper basement adjacent to the pumps old location. Still works like a charm. You sure steam isnt just blowing throw traps into the boiler feed pump? Especially since its cranked to 6 psi...
  • AndythePlumber
    it’s definitely blowing through traps into the feed reservoir, and because it’s 6 psi it’s also pushing through a wet return to get there
    THINK
    @AndythePlumber , I wonder if @Mad Dog_2 would come up there to consult?
    Consulting
  • AndythePlumber
    I would love to meet any of you dudes, I don’t think a site visit is necessary though. Honestly, I think someone put the feed pumps in when they put the addition on in the 50s and erroneously removed main venting while doing so thinking the reservoir vent would now vent the system…it’s all I got. There are no provisions for end of main venting while doing fittings installed. Most of the time you see an ancient tee with a plug in it. Or crossover traps that have been removed and plugged but the tee remains. Not the case here. What boggles me is that my local area techs have just kept doing the same thing over and over for generations of techs now
    THINK
  • AndythePlumber
    I really like your idea about two separate boilers, not gonna lie. We are going to be giving options. Perhaps sectioning some of the building for hydronic, but I hadn’t considered multiple steam boilers yet. Thank you
    THINK
    Consulting
  • Intplm.
    Intplm. Member Posts: 2,992
    @AndythePlumber Do you know if the original boiler was in a pit? Sunk into the floor? Have the replacement boiler, or in this case boiler"s" been placed above the pit?
  • MaxMercy
    MaxMercy Member Posts: 596
    That issue is why I've always wondered what the reason is for why steamers can't be built short and wide? (sorry for that clumsy sentence!!)
  • AndythePlumber
    The 6 x 11/4” 90 is gorgeous steamhead. Thing of beauty and even cast iron to boot. Top notch work brother! There is no known pit installations. The feed pump is recessed in a pit. One thing I must mention that I’m beginning to think is more and more important here. Of the two separate zones…
    The original homestead zone is the smaller, and the addition dated to the 50s is the larger and has the feed pump in a pit and the lions share of the wet return. Ok…
    The original homestead zone has a supply and a dry return with no operational venting or trapping and a drip connection to the wet at its end..
    The addition and larger zone has no dry return each radiator drops to the wet return all with rad traps in assumed failed operational conditions. Page 125 of the Dan’s Bible speaks on this and I’m trying to understand its significance here. I’m going to share some pictures soon…and wait till you guys see the pressure gauge it’s glorious and operational
    THINK
  • AndythePlumber
    IMG_4740.jpeg IMG_4747.jpeg IMG_4715.jpeg IMG_4713.jpeg IMG_4706.jpeg IMG_4717.jpeg IMG_4748.jpeg
    all I have for now. Is it possible to share videos?
    THINK
  • AndythePlumber
    these pictures illustrate what I mean about individual rads dropping to wet return. It’s the basement level of the addition. Wet return gravities to the recessed pump. Any basement level rads rad trap to the wet. All radiators have a trap in again unknown condition.
    THINK
  • AndythePlumber
    this is end of main on one end of the addition zone. Crazy water hammer can be seen here.
    THINK
  • AndythePlumber
    edited 4:57PM
    typically what you see at the pumps, I’m told it fills the room with steam a few times a week…
    THINK
  • AndythePlumber
    EOM and drip for the other side of the addition zone
    THINK
  • AndythePlumber
    dang
    THINK
  • ChrisJ
    ChrisJ Member Posts: 17,293
    That's an interesting gauge.
    It doesn't list it's units, but is obviously PSI, and it goes from 1-10 nice and linear and then that last 1 PSI amount of travel, ends up 30 PSI?
    EdTheHeaterMan Member Posts: 12,032
    That is what RETARD means on that gauge. Once the pressure rises above 10 PSI the gear ratio changes to move the needle at a reduced rate. When you want an accurate gauge in the lower PSI increments, but code says you need a 30 PSI gauge, this is the best of both worlds.
    ChrisJ
  • ChrisJ
    I thought retard meant if the needle exceeds 30 you need to reduce pressure.
    “RETARD” means the gauge movement is damped (slowed down) so the needle responds more slowly to pressure changes. A “retard” gauge has built-in damping or other modification to:
    • Reduce needle flutter
    • Smooth out rapid pressure fluctuations
    • Modify the arc at one end or the other end of the scale.
    • Make readings easier to see and interpret
    • Protect the internal mechanism from vibration and pulsation
    ChrisJ
  • ChrisJ
    Holycow I never noticed that before…. I knew they always say it, but never noticed how fast the pressure goes up.
    mattmia2 Member Posts: 16,446
    Are those wet returns? If they go to the condensate tank and the tank is lower than the return, won't they be dry returns, unless the pipe goes up then back down.
    Radiators that drop down individually to a wet return are usually 2 pipe air vent systems but those are early 20th century systems normally.
  • AndythePlumber
    I am considering them wet as they are just being ran across the floor and back pitched in many areas. By all means tell me if that’s flawed thinking. You can hear them just sloshing water around and hammering often
    THINK
    The back-pitch is the problem- those returns should slope down to the condensate tank. When that's done they will vent air as well. Then rebuild the traps and that zone should work.
    Consulting
    mattmia2Intplm.
    well, that and the 70 years of water hammer and 6psig has destroyed every trap in the system.
  • Intplm.
    ^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^ THIS ^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^