Weil McLain Gas Steam Boiler
Hello,
I have a brand new Weil McLain gas boiler with a Steam heating system. When asking for heat, the LCOW is constantly going off and water would be added to the system. Is this normal? I am not sure where I am losing water at. There is no leak unless at the radiator air vent that I hear hissing at times. What could be some potential causes for this. If the boiler is off, the water maintains its level and it does not overflow.
Update
I had added pictures of the slight glass with the boiler on ( right before LWCO is triggered) and after the boiler turns off and water returns. The Waterfeed is never triggered because it is set to a 2min delay and water returns past the LCOW level before that. I added a bit more of water using the bypass to increase the level and same result. Timed at 2minutes of heating before water level dropping and LWCO trigger.
Lots of reasons for this. More info required.
The first one that comes to mind is a bunch of pin holes or a crack near or just above the water line. This will allow the boiler to appear to operate normally while letting steam (that used to be water) leave the boiler and end up inside the exhaust vent. This would look like white smoke out of the chimney when the boiler is making steam. Since there is steam leaving the system, there needs to be water added to replace the missing steam.
The test for that is to turn off the burner and allow the boiler to cool off for 2 hours or more. Then add water so it goes above the gauge glass. See if any water starts to leak on the floor. You can fill the boiler with water but you don't want the water to get into the steam mains. Close the valve before the water gets too high. Just enough water to reach that leak so it spills out of any cranks onto the floor. Allow the water to remain that high for 30 minutes or until you see water.
If you don't find a leak that way, then let water out the drain valve until the water line goes back to the middle of the gauge glass before turning the burner back on.
Another common leak is the wet returns. Especially if they are under ground. Wet returns are any return pipe that happens to be below the boiler water line. Old iron pipes are noted for rotting away. And if they are underground, you will never see that leak.
Unlikely to be wet return issue, if problem is only happening while boiler is firing. It's a brand new boiler, so hopefully no leaks within the boiler itself. You can try to fill the boiler past the top, just to confirm. Do you have any hidden returns? Had this with a customer recently, with the boiler that I had put in a year or two earlier. Turns out there was a dry return, running through a crawl space, buried in dirt. Was leaking steam like crazy but nobody knew
Thank you all for your comments. No leaks within the boiler and we rerouted the return recently back in October. Interestingly enough a week after the return was rerouted, the boiler flooded and water was coming out of the main air vent at the return line. More than 20 gallons of water were removed and since then it has not overflow, I check the water level every 3-4 days. However, it short cycles because only enough water is added to meet the minimum level ( about half of the gauge glass) and then it igniters and a couple of minutes later water level drops and it short cycles with the LWCO going off. Should I increase the water feeder from its default setting of LWCO to 1 gallon? I have the VXT-24 auto feeder. Could it be that the boiler is oversized for the system? Or maybe contamination from the new return line that was rerouted and would need to be skimmed.
Post pics of boiler, near boiler piping, return work, radiators...as much as possible. Nobody can diagnose without info. All we could do is speculate every possible problem that could result in low water.
" I have a brand new Weil McLain gas boiler with a Steam heating system. "
New Boiler !!! Was it ever Skimmed ?
Has this been going on since the the install ?
I'd say the boiler needs Skimming to get the manufacturing oil out of the system.
The oil coating the top of the boiler's water causes eruptions sending the water out of the boiler tripping the LWCO, possibly eventually flooding the boiler due to water being added when the system as a whole (behaving normally) really does not need more water.
One Pipe System2 -
Thank you! I think this might be the cause as well. Looking at the VXT-24 auto feeder it has only had 4 gallons since its installation ( June 2025) and has been 4 gallons since October it might not be an actual water loss- unless that is not registering it correctly which it is also new. I will have to ask the contractor who installed it to skim it.
20 gallons removed Vs. 4 recorded makes no sense. Maybe you have multiple issues.
If it was never skimmed it probably needs it. And it may need multiple attempts since the oil was possibly blasted into the system by the eruptions and returns slowly.
One Pipe System0 -
@mb23 You need to post pictures. How does the sight glass look? Clean or dirty? Does the water level bounce when the boiler is steaming" Does it move more than an inch?
agreed, something does not add up. Maybe from the return at that time? It was really cold and temperature was set at 73 degrees during that week not sure if that helps. It was the only time it had that much water. All other times it does not overflow.
sight glass looks dirty (brown) but the water itself is clean( now). The water level bounces a lot while steaming until it finally goes to the level where the LWCO is triggered.
it’s carrying over and needs skimming as @109A_5 said
I have updated the post with pictures. What would be more beneficial, skimming or just a system flush?
follow up question, is the pressure trol suppose to be set at 15psi? The cut in is at 2 psi for residential home.0 -
Weil McLain but what model and size? Does Weil McLain have a different policy on which side a single takeoff can be? AFAIK all the others say it must be on the side with the controls so that you don't get nuisance triggers of the LWCO due to the probe seeing a false low waterline due to waterline tilt.
That second pressuretrol on the right is probably a manual reset high level cutout in the event that the primary pressuretrol set lower (1.5 to 2 psi) fails. I wouldn't set it at 15 psi though because that is where the 3rd backup which is the pressure relief valve is supposed to trip, making a mess possibly. Better to set it at maybe 5 to 10 psi.
I know this was posted before pictures "20 gallons removed Vs. 4 recorded makes no sense. " but this explains it
Are there 2 LWCOs on this system? which one operates the water feed? Why is the one on the right located on a pipe outside the boiler? I can see all kinds of problems that can happen with this setup
Not sure why the contractor put in two LWCO. The one that controls the feeder is the one on the left of the pressure trols. Not sure if redundant system? But the one on the boiler is the one that triggers the feeder, which it never actually is activated because the water is returned back into the boiler before the 2min delay. I have also tested and all the water returns to the level it was set to. It definitely has to do with surging. I added a bit more water 100% of the sight glass and I am timing how it takes to trip the LWCO ( 3 mins and trips) and water returns to its level in 45 seconds.
Does the LWCO just below the draft hood ever cause the burner to shut down due to a low water condition in that pipe?
No just the LWCO at the left of the pressure trol within the boiler. It is definitely due to surging water levels. I timed it to 3 minutes and pressure doesn’t get pass 0.50psi. It is physically seeing a lower water level and as soon as it shuts off water returns quickly. However the surging water level within the sight glass is the problem. Is there a difference between system flush and skimming?
Flushing means opening a valve or plug at the bottom of the boiler to force out any sediment that has built up on the bottom. A standard boiler drain valve cannot truly flush a boiler. It only allows water to dribble out through a small 3/8" opening inside the valve. To properly flush a boiler, you need a full-port 1-1/4" valve or larger so debris can be carried out effectively.
Skimming is done at the top of the boiler after it has been operated for several hours. You open a 1-1/4" (or larger) skim tapping and install a short nipple or pipe, typically 6 to 12 inches long. The purpose is to remove oils introduced during installation from cutting and threading pipe nipples and fittings.
When the boiler heats up, those oils end up on the surface because oil floats on water. This creates a thin film on top of the boiler water. That film interferes with proper boiling because oil has a higher boiling temperature than water. As steam bubbles form, they must push through the oil layer, which causes the surging you observe in the sight glass.
To remove that oil film, you need to create a gentle “waterfall” effect so that surface water flows slowly out through the wide opening of the 1-1/4" (or larger) skim port. The key is slow flow — just enough for the surface water to spill over and carry the oil with it. This process can take several hours the first time and may need to be repeated.
You cannot properly skim a boiler from a bottom drain. If you drain from the bottom, the oil on the surface will cling to the internal cast iron sections, similar to a bathtub ring. The goal of skimming is to prevent that residue from coating the inside of the boiler by allowing only the surface water to flow out gently through the skim port.
I hope this explanation helps.
Thank you Ed for the great explanation. This definitely means that the contractor did not skim the boiler after installation. I don’t think I even have a skim port.
you can see the skim hole in the boiler jacket to the right of the upper site glass valve, it still has jacket insulation there, which strongly suggests the nipple(valve) and cap were never installed, and no skim has occurred, your installer owes you,
or if you're handy, and with proper tools, , , , you'll need to skim more than once, do you have your manual?
there's a book sold on here, 'We've got Steam Heat", it's an easy read, and worth every dime,
known to beat dead horses1 -
I would love to purchase. Tried looking for it but no luck, do you mind sharing a link? Thanks!
Thanks! Just purchased. Anyone have any recommendations for a good contractor in Queens NY? I am not sure the installer is very knowledgeable with Steam heating and I would like to have the boiler serviced properly. It has been functioning like this all winter.
Yes, the LWCO was triggered ( please see picture with the yellow light) and a command was issued to the VXT. However, it never actually feed the boiler since the water returned before the delay (2 min) and the LWCO was satisfied and signal was reset.
also to @EdTheHeaterMan point, the second LWCO, the one on the pipe outside the boiler, did not ask for water as it is green in the picture with the VXT receiving the command from the LWCO at the boiler.0 -
So the LWCO on the pipe outside the boiler is a secondary Safety while the one actually in the boiler LWCO Tapping on the other side is the “operating” control. That makes sense.
So your boiler's burner goes off as a result of low water then the burner comes back on before the feeder adds water, and you want to know if this is normal. That depends on how your system is piped and operating. It appears that the LWCO is working. It appears that the delay on the water feed is set properly so your boiler does not get flooded. The only other question is, does the heat work? If the rooms are at or close to the thermostat set point, and you don't have banging, and/or you don't have hot and cold unbalanced room temperatures, then I might be inclined to say that for your system that is normal.
Is there any other problem that you want to share?
I might try to add some more water to the system. About 2 more inches up in the sight glass. The idea is that the burner should operate for two more minutes before the water level goes down below the LWCO and shut off the burner. Hopefully the returning condensate will start to return before the water level gets low enough to trigger the burner to shut off. If that stills cycles by the LWCO then you are stuck with a short cycling system.
Yes that is my question, is that normal. I am only getting 3 minutes of constant heat before it is shut off by the LWCO. It is a short cycle and I see that the LWCO is working fine and the sensor is fine but why does the water go down so quickly after 2 minutes of ignition. I also tested your theory to add more water, and set it to almost at the top of the sight glass and the timing was the same, 3 minutes and shut off. I can send a video if you would like to see it. Most of the time the rooms are evenly heated, except for the furthest room, however I added a T9 thermostat that continues to have its 24v supply interrupted due to this operation. I was under the impression the LWCO should rarely trip. I also do have water hammering.
Does it still need skimming? It should help with the surging I am guessing.
If your boiler's burn period is being interrupted by the water quickly and significantly leaving the boiler and tripping the LWCO, I'd say it needs skimming, especially since it appears the pipe typically installed to do the skimming was never installed.
One Pipe System1 -
No way it is normal function. You are getting carryover and probably a tilting waterline. The boiler was piped incorrectly with the takeoff on the far end from the controls, when it should be on the closest end to the controls. Especially when the water gets low, the waterline tilts towards the side of the boiler with the takeoff causing the probe to be exposed even if the average waterline would be above it without the tilt. You may need to flush out the returns along with skimming and draining and flushing the boiler.
I am surprised you aren't hearing any noises like gurgling radiators or spitting air vents or banging.
I am getting banging at the boiler in the main, the feeds and sometimes at the boiler. It was greatly reduced when the return was rerouted.
Thank you all for all this very helpful information. Also thank you for suggesting the book. First time homeowner and the boiler was changed from oil to gas back in June 2025 but the steam system was never changed. Sounds like I need some big maintenance items. Hopefully installer is able to do it and it is not a big cost.
The installer should have done the initial skimming, so I would think they owe you that. The change to the return may have added additional oil to the system (depending on the pipe type used) so skimming may have needed to be done after that also.
One Pipe System0 -
Since your boiler has probably been puking oil up into the rest of the system for some time now it would not surprise me if your boiler will need skimming multiple times as the oil slowly returns to the boiler over time.
I'd get the skim pipe installed, a full port ball valve would be nice too. And learn how to do the skimming so you are not paying for return trips of a contractor.
One Pipe System0