Weil McLain Gas Steam Boiler
Hello,
I have a brand new Weil McLain gas boiler with a Steam heating system. When asking for heat, the LCOW is constantly going off and water would be added to the system. Is this normal? I am not sure where I am losing water at. There is no leak unless at the radiator air vent that I hear hissing at times. What could be some potential causes for this. If the boiler is off, the water maintains its level and it does not overflow.
Comments
-
Pics?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Lots of reasons for this. More info required.
The first one that comes to mind is a bunch of pin holes or a crack near or just above the water line. This will allow the boiler to appear to operate normally while letting steam (that used to be water) leave the boiler and end up inside the exhaust vent. This would look like white smoke out of the chimney when the boiler is making steam. Since there is steam leaving the system, there needs to be water added to replace the missing steam.
The test for that is to turn off the burner and allow the boiler to cool off for 2 hours or more. Then add water so it goes above the gauge glass. See if any water starts to leak on the floor. You can fill the boiler with water but you don't want the water to get into the steam mains. Close the valve before the water gets too high. Just enough water to reach that leak so it spills out of any cranks onto the floor. Allow the water to remain that high for 30 minutes or until you see water.
If you don't find a leak that way, then let water out the drain valve until the water line goes back to the middle of the gauge glass before turning the burner back on.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Another common leak is the wet returns. Especially if they are under ground. Wet returns are any return pipe that happens to be below the boiler water line. Old iron pipes are noted for rotting away. And if they are underground, you will never see that leak.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Unlikely to be wet return issue, if problem is only happening while boiler is firing. It's a brand new boiler, so hopefully no leaks within the boiler itself. You can try to fill the boiler past the top, just to confirm. Do you have any hidden returns? Had this with a customer recently, with the boiler that I had put in a year or two earlier. Turns out there was a dry return, running through a crawl space, buried in dirt. Was leaking steam like crazy but nobody knew
0 -
Thank you all for your comments. No leaks within the boiler and we rerouted the return recently back in October. Interestingly enough a week after the return was rerouted, the boiler flooded and water was coming out of the main air vent at the return line. More than 20 gallons of water were removed and since then it has not overflow, I check the water level every 3-4 days. However, it short cycles because only enough water is added to meet the minimum level ( about half of the gauge glass) and then it igniters and a couple of minutes later water level drops and it short cycles with the LWCO going off. Should I increase the water feeder from its default setting of LWCO to 1 gallon? I have the VXT-24 auto feeder. Could it be that the boiler is oversized for the system?
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 117 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements