Should I even think heat pump is an option ?
Older two story on slab with attached garage. Infloor on the main and garage, air handler upstairs. Design temp is -21f (-29c) and heat loss calc says I need about 70k. No a/c , but we would love to have.
25yr old cast oil boiler now, 110k output. Its running fine, but ya know.. 25 years. Two (of 7) wirsbo valves are stuck open (need new manifold) , needs a new mixer, a couple of the old gate valves are kaput. So, Id like to repipe and go more efficient this summer.
My options seem to be:
  1. New oil boiler, repipe and add buffer tank . Cheapest solution for up-front and long-term maintenance costs, but most expensive for fuel.
  2. New mod/con gas boiler, repipe and add buffer tank. Save a ton on fuel costs, but high up-front and maintenance. Parts for these things are $$$, it seems.
  3. New ccHP (A2W) plus propane Aux heater of some sort , both feeding into a buffer tank. I havent priced this yet, but I suspect it would be large. Fuel cost would be lowest. Bonus: We would get a/c.
I put propane as aux, as going electrical Aux would be pricey anyhow. The existing electrical service is only 125a. Would need new overhead wires and panel (I diy'd original, should have put a 200a panel on.. who knew).
Am I crazy to even think of a ccHP for A2W in this climate ?
    hot_rod Posts: 28,708
    Unless your heat emitters can cover the heating load on the design, -21F?? day, with 120F SWT, I would say no. That 70K load is a bit high also.
    Here is some info from Arctic on their cold climate models. A2WHP manufacturers have become a bit more realistic on how their systems can or cannot replace a boiler.
    Screenshot 2026-01-25 at 9.30.40 AM.png Screenshot 2026-01-25 at 9.32.19 AM.png
    I think you would regret a HP. If you mechanically and electrically inclined a MOD CON would be the best choice.
    Learn your own system and you can do most of the service and maintenance better that most so called techs now.
  • Hot_water_fan
    Hot_water_fan Posts: 2,249
    I think the easy solution for upstairs is heat pump + furnace. You don’t need hydronic for forced air.
    Also, how much oil did you use in the last fill? 70kbtu is a LOT.
    pecmsg Posts: 7,634
    I like the heat pump installed here but change to hot water cast iron radiators when it gets below 35° outside.
  • Gabriel82
    Gabriel82 Posts: 39
    @Dave Carpentier I had some photos of heat pumps on the inside...
    It was scary: they are computers big freezers things style "heaters"...
    So much electronics...
    Sure is nice to be able to "call your central heating unit" from 2000 miles away and tell it to start heating.
    But they are complex ,and with no heating back-up I can't even imagine in what temperatures you might have to live in(plus no hot water) if the damn thing fails in minus 10-20 Celcius blizzard...
    You alone ,will not be able to fix it. That I know for sure...
    As for big water buffer storage tanks ,they are indispensable.
    They work like big batteries and store excess heat for at least 12 hours.
    Even if your heater fails you will still have heat +hot water in house for a few hours just using the excess heat energy stored in those big insulated water tanks.
    I tend to be inclined toward energy security and independent problem fixing!
    You can do that in an oil heater.
    I don't see doing that with a heat pump.
    They either work or don't.
    And in a bad weather period how or will the tehnician get to you if the heat pump has a problem?!
    Of course ,it's your choice!
    SuperTech
    pecmsg Posts: 7,634
    The only computer on mine is the T-Stat!
    Minis have quite a few.
    VRF and Commercial have even more.
  • Gabriel82
    Gabriel82 Posts: 39
    I've had such problem in a blizzard minus 16 Celcius, no electrical power for about 14-16 hours...
    Because snow was pilling up around 3 meters tall/deep I had to get all my clothes on and wait it out...
    Needless to say ,in spring, I had myself built 2 ceramic tile stoves with natural draft chimneys storage space in house for 2 tons of very dry wood briquettes plus enough firewood for 2 weeks!
    I woke up one Sunday morning next winter, never even knew there was no electrical power + minus 11-12 Celcius outside...
    But felt it on my skin when opened the outside door 😳
    It's good to be warm and safe 😂
    Why depend on others?!
  • Sorry, I kept meaning to come back and reply to this..
    Yes -21f design temp (we're north of minnesota).
    We're almost at 500 gallons of oil used so far this year. We typically burn 525-625.
    I used the SlantFin app to get the 70k heat load, it was more like 62k but I hedged my assumptions a bit. I dont think I would install anything under 80-90k though.
    I hadnt really thought about the very low SWT from a HP and if that would cover my demands for even the day/night swings of the non-peak parts of the winter.
    So, Im certainly back to presuming a modcon.
    HVACNUT Posts: 7,785
    I wouldn't get rid of the current boiler setup and rely solely on a heat pump.
    How does the house lay out? Are there areas to drop ducts from the attic to the first floor ceiling? Keeping the hydro coil while adding a properly sized and zoned 2 stage heat pump would decrease oil consumption. Two thermostats downstairs, keeping the radiant seperate. Upstairs, the hydro coil can be auxiliary. You'd have to compare that to the electrical rates.
    As far as the boiler, there's options where you keep the oil and still gain efficiency. Is LP gas cheaper than #2 fuel oil by you?
  • winnie
    winnie Posts: 80
    Heat pumps work best when the differential temperature between heat absorbed and heat released is smaller. So an air to water heat pump really wants to use lower hot water temperatures than your underfloor system is probably designed for.
    Your underfloor system also probably won't be particularly useful for AC :) So to get AC you are talking about adding ductwork or air handlers to the first floor in addition to adding the heat pump.
    At that point you might as well consider completely separate heating and AC systems.
    I know that I sound like a broken record on this, but I think you will be best served with a fuel burner for heat and minisplits for air conditioning, and if the minisplits give you some shoulder season heat then that is a freebie.
    Steamhead
  • Kaos
    Kaos Posts: 1,003
    edited February 19
    Based on the amount of oil you burn, that Slant fin heat calc is about twice your actual heat load. If you want more accurate number run through the math here:
    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
    Assuming your heat load is around 36000BTU and your slab pipe spacing is reasonable so you don't need very warm water, -20F is well within the reach of air to water units. Whether this makes sense depends a lot on your local energy costs and what you can get the unit installed for.
    This or something similar is probably in the ballpark:
    https://media.us.lg.com/m/3a43e47d816724b3/original/SB_AWHP-Monobloc_KPHTC481M-pdf.pdf