MM#67 and feeder compatibility
Current boiler is a Crown gas Steamer…
Not that old but it has a MM67 float type lwco.
The feeder is a Unimatch WF2-U-24
Customer complains that the feeder overfills each time lwco is triggered.
There are no settings on the feeder to limit the water.
VXT should allow more control correct?
  • JUGHNE
    JUGHNE Posts: 11,633
    Can you throttle the flow out of the feeder?
    I do that when the boiler feed pump is too aggressive and jiggles the float to shut off the burner. I use the iron quarter turn plug valves which I reclaimed from gas lines when replacing those with ball valves.
  • kcopp
    kcopp Posts: 4,714
    Tried that. No dice.
  • Big Ed_4
    Big Ed_4 Posts: 3,569
    I remember dip switches in the Unimatch where you set it for the 67 ..
    EBEBRATT-Ed Posts: 20,941
    Water level bouncing?
    I looked it up. Discontinued and replaced by a newer control.
    It is supposed to have a 3 position slide switch to change the timing.
    The newer control has something similar and also has different orifices to change the flow rate.
  • kcopp
    kcopp Posts: 4,714
    Im sure the orifices are LONG gone.
    That 67 switch is it. No delay or timing for cycle.
    EdTheHeaterMan Posts: 12,690
    if you need better control the Unimatch WF2-U-24 can be replaced by a VXT. If throttling the water thru the Unimatch WF2-U-24 is not getting you where you need to be.
    kcopp
    109A_5 Posts: 4,363
    edited February 13
    https://inspectapedia.com/heat/McDonnel-Miller-WF2-Water-Feeder-Instructions.pdf
  • kcopp
    kcopp Posts: 4,714
    Thanks. Confirms my thought that this "uni match" is not a good match for the system.
    109A_5 Posts: 4,363
    I would think with the correct orifice it would work great.
    The orifice with a VXT is about a Gallon a minute. If a Gallon a minute is too much a VXT may over fill the boiler too.
  • Big Ed_4
    Am I correct , if you throttle that unit down with the valve it sticks open ? I could be wrong but I think I tried that and found out ….
    109A_5 Posts: 4,363
    That may depend on where the manual valve is. The orifice is probably in the correct position for the solenoid valve to work correctly.
    Was the float functionality in the M&M 67 verified to work correctly ? The M&M 67's water level range of 'Call for Water' to 'I'm satisfied' should be very narrow. Sluggish float movement may mess up any water feeder causing it to over fill the boiler.
  • kcopp
    kcopp Posts: 4,714
    Float works well.
    Its flushed often as the system is drained out when it overfills through the 67.
    Do they have higher than normal water pressure?
    109A_5 Posts: 4,363
    @EBEBRATT-Ed I like where you are going with that but over 150 PSI, Wow !!!
    I'd troubleshoot the issue until I understood what was causing the actual problem. Then determine the proper course of action for the repair.
    @109A_5
    I learned long ago not to trust what the mfg. says 100%. I would not trust one of those to hold 100% at 150.
    109A_5 Posts: 4,363
    @EBEBRATT-Ed Yes I understand, for me it is a starting point reference.
    Is the fill time for only 60 seconds, does the orifice actually exist… Understanding the actual cause of the problem makes for better repairs.
    Would have been nice if the manual gave more information about the actual orifice size and where it is so you don't have to take the whole thing apart it check it.
  • kcopp
    kcopp Posts: 4,714
    The water pressure is 60/70 psi.
    I have not started pulling the feeder apart but given that he has to dump water from the system Im sure they are missing.
    109A_5 Posts: 4,363
    Is this a new problem or has it been that way since the feeder was installed ?
  • kcopp
    kcopp Posts: 4,714
    Not sure.
    Im the 3rd guy in and he is not the original owner…
    109A_5 Posts: 4,363
    Looks like the orifice is on the outlet side of the solenoid valve. Thanks @Gordo
    McDonnell & Miller Uni-Match S-45 Valve Teardown. Water Feeder For Steam Boiler
    https://youtu.be/GD5QmoNLirU
    kcopp
    109A_5 Posts: 4,363
    edited February 15
    Hydrolevel's VXT Service Kit #45-345 For Rebuilding Their Steam Boiler Water Feeder Valve
    There is more than one uni match model. Not sure if the older ones had the orifices.
    109A_5 Posts: 4,363
    I believe I was using the orifice information from the correct manual (link posted above), from the model number provided. I'm assuming it is 24 VAC burner circuit unit. Maybe the orifice was removed or the valve leaks.