MM#67 and feeder compatibility
Current boiler is a Crown gas Steamer…
Not that old but it has a MM67 float type lwco.
The feeder is a Unimatch WF2-U-24
Customer complains that the feeder overfills each time lwco is triggered.
There are no settings on the feeder to limit the water.
VXT should allow more control correct?
Comments
-
Can you throttle the flow out of the feeder?
I do that when the boiler feed pump is too aggressive and jiggles the float to shut off the burner. I use the iron quarter turn plug valves which I reclaimed from gas lines when replacing those with ball valves.
0 -
Tried that. No dice.
0 -
I remember dip switches in the Unimatch where you set it for the 67 ..
There was an error rendering this rich post.
0 -
Water level bouncing?
I looked it up. Discontinued and replaced by a newer control.
It is supposed to have a 3 position slide switch to change the timing.
The newer control has something similar and also has different orifices to change the flow rate.
0 -
Im sure the orifices are LONG gone.
That 67 switch is it. No delay or timing for cycle.
0 -