Mixing Valves and Pumps
Hello. My actuator that controls the mixing valve stopped working last year, and now my mixing valve seems to get stuck when turned all the way clockwise. Instead of replacing the valve and actuator we tried to find a point where the radiant temp was 120 and leave the valve there. I was told I needed a new pump. We had a new pump installed which is now causing noise in my other pump. My temp going to the floors is now at 170. This leads me to the following questions:
- In this setup, should I replace the mixing valve and actuator?
- If I don’t replace, what should my mixing valve be set to?
- If the valve is all the way clockwise, will that stop sending water to my radiant pump?
- If the valve is all the way counter clockwise, will that be too hot for my radiant?
Thanks all. Pics attached
Comments
-
Yes, the valve should rotate fairly easy. If it jams, it could ruin the actuator.
You can operate it manually, get the boiler up to temperature, run the zone pump and adjust. This is refered to as a "dumb" mixing valve. It will not respond to the control and be able to adjust the water supply temperature.
It is a fairly simple valve under the hood, easy to disassemble. However if the rubber o-ring seal is worn or hardened, it may not last through a disassemble and reassemble. Example of a 3 port version below.
I believe it is an ESBE valve and a repair kit, and new actuator may be available.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Sort of. The mixing valve is to set or adjust the temperature of the circuit following it. The way it works is you have nice hot water — hot enough for the highest temperature demand in your system. But some other part (notably your floors — 170 is much too high) — needs cooler water, so you mix some of the hot source with some of the cooler returning water to get it "just right" and then send it on its way with the pump.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
there are 3 components to that valve. The valve, an actuator and a control. I suspect that white tekmar control was wired to the actuator?
The valve blends down the high temperature from the boiler to a lower temperature for the radiant.
In some cases, depending on the control it could also be protecting the boiler from too cold of return water. So it can be a dual purpose valve.
Definitely worth getting rebuilt or replaced to get the best use of the system
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@Jamie Hall thank you. We ran out of hot water today so I thought I’d play with the valve manually while I look for somebody to replace it and the actual. When I turn the valve all the way clockwise, the pipe to the floors immediately cools down. Same thing when I turn all the way counter clockwise. @hot_rod yes the Tekmar control was connected to a blue actuator picture attached
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements