Weil mclain combi circulator wont turn off
Circulator pump runs constantly, even when no call for heat from thermostat or the bypass wire at boiler.
Recently replaced expansion, relief valve, water feeder, and 3 way valve. Circ pump only turns off when disconnected from 1107-1 brain. Otherwise, pump runs constantly.
Replace brain? It has already been replaced once. 12 yr old unit.
  • Could be 3 way valve. We disconnect 3 way valve, circ pump stops.
  • Argh!!!! We found 3 brains on shelf and 3 old 3 way valves! No wonder they discontinued this combi!
    hot_rod Posts: 28,347
    When that many components fail in a short period of time, it might be time to troubleshoot the troubleshooter.
    Failed waterside components are often directly related to the water quality, both boiler side and potable water side.
    Tankless and combis in hard water conditions need occasional descaling, preventive maintenance. Boiler side water needs to meet the spec in the manual.
    They are not at all like a tank water heater when it comes to hard or aggressive water.
    GGross
    109A_5 Posts: 4,497
    edited December 2025
    What LEDs are presently on with the circulator constantly running?
    109A_5 Posts: 4,497
    Sounds like the 3-Way valve. Since its End Switch can directly produce a call for heat.
    Personally if it was my boiler, since the 3-Way valve seems to be a chronic issue I'd replace it with another (different) 3-Way valve or two Zone Valves one Normally Open and one Normally Closed. An interfacing electrical wiring harness would have to be made.
    Sadly this is beyond the scope of most HVAC contractors and Plumbers. And then there is the dreaded liability thing.
  • kcopp
    kcopp Posts: 4,718
    Is this a CGt?
    I have had the issue where the heat stays on w/ the Honewell 3 may valves. This will happen if the valve gets stuck. Water quality often tends to be the issue.
    109A_5 Posts: 4,497
    @kcopp I believe it is a CGt.
    Must be so some pretty bad water if a new valve is getting stuck within weeks of replacement. I would imagine much of the water was replaced to change the valve.
  • kcopp
    kcopp Posts: 4,718
    Duplicate post…
  • Multiman
    Multiman Posts: 38
    I am so discouraged. When looking around, we found on the shelf nearby THREE old brain boards, and THREE old three way valves. This is a unit that is about twelve years old. No wonder Weil Mclain discontinued it.
    The water is city reservoir water, considered to be good quality water, although some have said lately that there has been more of a problem with sediment. These are ancient triple deckers in an old factory town; I'm not going to put a whole house water filter on it, nor am I going to put an in-line filter on for this particular unit.
    Some twelve hundred dollars at least over the last six months in repairs. So frustrated. I asked my HVAC plumber to price out a replacement. I'll make a separate post for recommendations for replacement.
    109A_5 Posts: 4,497
    The thing is, if water quality is truly the underlying issue and the "brain boards" and three way valves were all swapped out in sets each time the unit acted up, a water filter may be your the best defense. Sediment may cause the valve to stick. If the water is that poor as far as heating equipment goes a new boiler may have its own set of issues from the water quality issues.
    Has the water been tested and compared to the Weil McLain specification for that boiler ?
    For better or worse and for various stimulus reasons, but mostly Engineers like to eat and have a roof over their heads. So to eat and have that roof they need to get paid. So they keep coming up with new and different designs, some better than others.
    Since there is so many parts lying around, if it was me I'd be figuring out what the issue with the sticking valve is. I do realize not everyone can do that.
  • kcopp
    kcopp Posts: 4,718
    Dont confuse the water from the town as the system water. System water is a closed set up.
    The CGt (if that is the unit… still didnt get confirmation) The 3 way valve is on the closed part of the system.
    3 way valve does not touch the city water. tell us more about the system… baseboard? cast iron rads? convectors? What is the piping to everything like? Pex? copper? Polybutylene?
    I am 99% sure its not a board issue. The cartridge on the 3 way is easily replaced.
    109A_5 Posts: 4,497
    @kopp Don't they use city water to refill the system every time the valve fails and needs to be replaced ? Potentially adding a new load of bad stuff to help ruin the new valve.
  • kcopp
    kcopp Posts: 4,718
    Not that much water…. maybe 2 gallons to top it off.
  • Baseboard with all copper piping. The city water is generally very good. But I do think that there was fairly recently some issue with cloudy water with the city flushing all the pipes - I doubt that coincidentally that would have been the same day that the water went in. I do know that the water that came out was dirty looking, when they drained it.
    The valve that the plumber put in is a Honeywell VC8710-03. The system is a Weil Mclain discontinued combi, cgT 5 pin series 2, made in 2014. We tested all the connections, and it's clearly that the valve has failed yet again, is stuck on open yet again.
    The quotes for replacement are insane. Pretty much everything on this unit has been replaced recently, in like the last 6 months - the 3 way valve, the expansion tank, the overflow relief valve, the water intake actuator. I only wound up with managing this building about a year ago, and have no communication with the previous mgr, just know from his asst that the unit has always been problematic.
    I am quite sure that the plumber would have refilled the system with city water. Certainly, if there were a way to get the water in, I could use distilled water to refill it.
    Is there a better 3 way valve to use as a replacement?
    109A_5 Posts: 4,497
    Seems the Honeywell VC8710-03 has been discontinued and that is just the actuator not the actual valve.
    Seems the replacement actuator is " 3-Way Valve Actuator for CGT Boilers, 635-100-023 "
    https://www.supplyhouse.com/Weil-McLain-635-100-023-3-Way-Valve-Actuator-for-CGT-Boilers
    However if the actual valve is sticking just changing the actuator may never help.
  • kcopp
    kcopp Posts: 4,718
    I ended up w/ two of these swapping out the wiring harness and converting out the CHt to a CG… I then installed an electric WH.
    In effect you disable the valve actuator, push the cartridge into the heat only mode and the wiring is removed so it will not be used and the combi any longer.
  • Multiman
    Multiman Posts: 38
    kcopp, I think that is my next step, to converti it over to heat only, and separate out the domestic hot water, if this 3 way fails yet again. I sent you a message.
    Jamie Hall Posts: 27,818
    For better or worse, a couple of comments. First, a water quality problem won't fry a computer board. Second, having three of a specific c component fail over a short period of time is a bit suspicious. Once in a while you do get a bad run of something. Sometimes you get a failure prone design.
    But…
    Very often there is an underlying problem which is the root cause, and without figuring out what that is one will keep having problems.
  • Multiman
    Multiman Posts: 38
    Not the board, this time. It 8s the 3 way valve itself stuck on open. New one Worked a couple of months, then failed again.
    109A_5 Posts: 4,497
    Was the guts of the 3-way valve ever been changed, or just the actuator ?
    If this was my boiler and the 3-Way valve (assembly) is a chronic failure but the boiler and the DHW all works fine, I'd get rid of the 3-Way valve and use two Zone Valves a Normally Open and a Normally Closed to replace the 3-Way valve, probably way more reliable.
    That looks like a spring return 3 way zone valve
    It would be very rare for one not to close when power is removed. Does motor fail? The gear train?
    If the stem is seizing I would run a cleaner in the system to address water quality
    I would not repipe it with two valves until you determine the cause of the failures
    Certainly not a NO zone valve, they tend to have a shorter life span
    I would try another brand of 3 way before you repipe with two valves and double the failure potential.
    109A_5 Posts: 4,497
    edited February 6
    Well you certainly could use two Normally Closed zone valves, it just complicates the wiring a bit, since you need to prove the zone valve that is used for the 'open' part of the 3-Way valve (DHW) has actually opened before the burner fires. Not really a big deal if you can do control wiring.
    It appears the original 3-Way valve does use its End Switch for the space heating mode.
    Personally I think the CGt is a failed design as far as the 3-Way valve is concerned. They have updated the 3-Way valve assembly and it appears folks are still having issues. You could try another brand of 3-Way valve, not sure about compatibility. You could also go the route of separate DHW production, but to me with a bit of ingenuity the CGt could be made more reliable and still be used as a Combi.
    109A_5 Posts: 4,497
    edited February 6
    With two Normally Closed zone valves.
    If the building actually has other zone valves the Normally Closed zone valve for space heat at the boiler is kind of redundant.
    Instead of modifying the boiler's control wiring it may be simpler to just use a zone valve controller.
  • epmiller
    epmiller Posts: 59
    @hot_rod Not to hijack the thread but with my limited exposure to N/O zone valves, why do you say they don't last as long? I just had to make up a '3-way' assembly for a system using Taco Zone Sentry valves (one already existing) and I can't see why the added N/O valve will not last as long. My only complaint is that the end switch doesn't have NO contacts.
    109A_5 Posts: 4,497
    edited February 7
    Building off of " Instead of modifying the boiler's control wiring it may be simpler to just use a zone valve controller ".
    Remove the 3-Way valve.
    Add two Normally Closed zone valves. Or just one for DHW boiler circulation if other space heat zone valve(s) exist.
    Add a zone controller, if needed, if one does not already exist.
    Disconnect the wires from the boiler's Low Limit switch, the wires become the Boiler's T-T to the zone valve controller's X-X (Isolated End Switch).
    The boiler's Low Limit switch is wired to the zone valve controller's DHW priority input. DHW priority is set to active.
    The space heat thermostat(s) and space heat zone valve(s) are connected to the other zone controller zones.
    The system behaves like an Indirect tank is being used with zone valves, however there is no Indirect tank. Just boiler only circulation for DHW priority and the original thermostat(s) control the space heat zone valve(s).
    It should have the same reliability as any other zone valve system with Normally Closed zone valves.
  • kcopp
    kcopp Posts: 4,718
    Here is the Weil info and the part I ordered.
    This is the simplest and less aggravating option. IMO.
    I got this from Weil about two yrs back.
    109A_5 Posts: 4,497
    Curious, is electricity inexpensive in your neighborhood ?
  • kcopp
    kcopp Posts: 4,718
    Not terrible.
    Cheaper for the landlord vs replacing the boiler.
    I was the 3rd contractor in making repairs.
    Tenants were coming home to a home at 85F frequently.
    109A_5 Posts: 4,497
    OK, I would never seriously recommend replacing a good boiler, just change the 3-Way valve blunder.
    edited February 7
    With 8760 hours in a year a zone valve would be powered on maybe 2000- 2500 hours, spring returned the rest
    With a NO valve it is under power many more hours, basically a stalked motor. So motor life is shorter
    Pretty much all combus use some dort if three way . Many have a composite block with pump, hx, and valve in one component
    There have been a few combis with a separate pump for the dhw plate hx
    That Taco is a capacitor discharge valve I believe ? Does it have any power consumption in either open or closed position? Or just when it travels?
  • kcopp
    kcopp Posts: 4,718
    As I said I was the 3rd person through. The valve guts and powerhead had been replaced several times. After a couple years it was getting old….
    Im sure it is getting old for the OP.
    In the memo from WM they do mention that this is an issue and they had been getting many inquiries on doing just what I did.
    Disable and add a different way to get hot water was the logical choice…
    Everyone is happy.
    109A_5 Posts: 4,497
    @hot_rod
    " With a NO valve it is under power many more hours, basically a stalked motor. So motor life is shorter "
    OK I'm confused, I would think a NO valve is open until powered, once powered it closes.
    For example, one half of a 3-way valve is open when not powered and the other half of the valve is closed. When powered the NO and NC change state.
    109A_5 Posts: 4,497
    I understand why that resolution was used. However, to me it just seems like that is the second most expensive (initially and over time) resolution.
  • Multiman
    Multiman Posts: 38
    Thank you to all, really, very much for all the input. All of you think like engineers, some of you probably are!
    I replaced the Honeywell 3 way valve yet again, and all is well… but the previous 3 way valve only lasted two months or so! My plumber says that he can easily put in a separate gas fired hot water heater for domestic hot water, that there's room for it, and the connections will be easy to do, so if it fails again, I'm going to take kcopp's advice and convert the combi over to running the baseboard hot water heat only.
    BTW, I'm in central CT, if anyone who has successfully done this conversion already wants to do another!
    kcopp
  • epmiller
    epmiller Posts: 59
    Yes, Taco Zone Sentry valves only consume power when they are moving. So I'm not going to concern myself about a reduced lifespan for my situation. I can easily see why a standard spring return valve that is constantly powered to hold it open would not last as long. I'd hate to install a spring return valve in a constant ON state given all the power it would consume just holding it in the "normal" state.
    109A_5 Posts: 4,497
    I think you would find with Normally Open valve, the valve is actually Open even when it is in its box from the supply house, electrically connected to nothing. The spring return actually opens the valve. When it is powered it closes the valve.
    Normally Open is the quiescent state or when inactive.
    Taco Zone Sentry are a different technology than a conventional zone valve. Still they still consume power to keep them in the non-quiescent state.
    109A_5 Posts: 4,497
    @Multiman you and your contractor can do what ever is best for your situation. I just like to provide the least expensive alternatives to what appears to be poor OEM engineering. Sometimes my alternatives may be too complicated or surgical for the average Plumber. However I posted them anyway, providing options, maybe a DIY homeowner would benefit from them.
    Where I live electric heating of anything is expensive compared to NG. Historically NG water heater tanks are installed and last the best part of 20 years with only one thermocouple replacement (if any). With the new electronically controlled gas valves it may put them in a higher maintenance cycle like Electric heating elements.
  • epmiller
    epmiller Posts: 59
    @109A_5 thanks for that spec sheet on the Zone Sentry valve. Somehow I didn't find all those details about power consumption when operating. I still have no worries about how I used the valve in the installation, it only gets called once or twice a day during the heating season for about 15 minutes. Pretty low power drain.
