Beckett Burner tripping

Options
JayS
JayS Member Posts: 4
edited January 29 in Oil Heating

For approximately the past month, the burner on my New Yorker boiler has been intermittently tripping. Typically, resetting it is easy: pressing the red reset button on the Honeywell ignition control will restart the burner, often with just a touch. However, on occasion the reset button alone does not work.

When this happens, I’ve observed that gently tapping on the transformer will cause the burner to start. Based on this behavior, I suspected a bad transformer and replaced it.

But, replacing it, did not change anything!

What the heck is going on!

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769

    You may have a dead spot on the motor. if there is power to the motor and the transformer and the motor does not operate then the tap may get the motor to start and off you go. The problem with that repair is: if my guess is incorrect then you now own two good transformers and two good motors. and you still have teh problem.

    Have you thought of calling a professional oil burner technician?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    kcoppIntplm.
  • Gabriel82
    Gabriel82 Member Posts: 19

    I have to ask : why not Becket designed and built a brushless DC motor for their burners?

    At least the 24 volt version I know of.

    And why no big(above 10Kwh) burners use a brushless DC motor?

    They seem to be very reliable in many commercial things(cars and electric motorcycles beeing one).

    Plus one can very gradually adjust speed of fan or oil pump unlike present AC motors...

    Bad to the Bone

    Song by George Thorogood & The Destroyers ‧ 1982

  • HVACNUT
    HVACNUT Member Posts: 7,312

    If the primary is the long obsolete R8184G, then the tap to the transformer to resonating to the primary. Bad relay contacts. Your service provider could upgrade it. Possibly add an oil delay valve too for cleaner ignition.

  • HVACNUT
    HVACNUT Member Posts: 7,312
    edited January 29

    @Gabriel82, Yes, I believe it can be easily done.

    But you'd need more than just a modulating burner. Picture the scales for setting combustion air, pump pressure, and the "Z" dimension as 1 to 10 settings. High fire is 10. Low fire is 1. Every adjustment to modulate down can't always be 9 on air, 9 on pump pressure, 9 on Z. 8 and 8, and 8, and so forth. The actual combustion would need to be constantly monitored, and feed that information to the burner to make proper adjustments to the ratio to stay clean burning through the whole range.

    They probably have a prototype out on Highway 61 next to the forty red, white, and blue shoe strings, and the thousand telephones that don't ring.

    Gabriel82
  • MaxMercy
    MaxMercy Member Posts: 570

    I just had the same issue on a Honeywell R8184G controller running a Beckett on a recent property acquisition on a freezing (of course) Sunday night (of course). When the reset was pushed, nothing would appear to happen but the safety would pop after 45 seconds.

    I disassembled the controller and found a dime size hole burned in the PC around a relay contact that powers the burner motor. To repair, I removed the relay, Dremeled out the burned area, filled with epoxy, drilled a new hole, installed an extension wire to replace the relay pin burned below the PC level, and reinstalled. At some point I'll update the controller to a Carlin 70200.

    If yours is intermittent, it could be a bad solder joint starting. Once the gap widens, it starts an arc which will burn a hole in the board.

    One thing you don't want to do is keep pushing the reset unless you figure out the problem.

  • Jamie Hall
    Jamie Hall Member Posts: 27,026

    On @Gabriel82 thoughts about motors. Quite right. In the last decade or so brushless "DC" motors (they are actually rectifying AC motors, but we'll let that go) have become the go-to. But we still use AC induction motors for a lot of applications. Why? Cheaper. Long life spans (decades). Reliable. Run on crappy power. Perfectly satisfactory for constant speed applications (which includes domestic oil burners). If it ain't broke…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Intplm.EdTheHeaterManGabriel82
  • Intplm.
    Intplm. Member Posts: 2,917

    A typical scenario. The tapping (yes even on the transformer) moves the motor ever so slightly off of the dead spot of the winding and, wa-la! the boiler starts. "What the heck is going on?" This stuff can make you crazy.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769
    edited January 29

    Cost

    If you understand how a fuel pump create pressure then you would know that adjusting the speed of the motor will not produce the desired effect. that being a change in the pump pressure to the nozzle in order to change the BTU input in some way that can be matched by change in air flow that a fan might produce when the fan rotation speed is changed.

    To your point, since Gas input can be adjusted by way of a variable negative pressure at the gas valve, the DC motor IS being used in just that manor to offer variable input burners incorporated into many condensing boilers that operate with Natural and LP Gas.

    You should do more research with liquid fuel burners to see if you can invent one that is cost effective with a DC motor that can also adjust the liquid fuel pressure to match the variable combustion air input available with such a DC motor option. Let me know how that works out.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Gabriel82
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769
    edited January 29

    @MaxMercy said: "I disassembled the controller and found a dime size hole burned in the PC around a relay contact that powers the burner motor. To repair, I removed the relay, Dremeled out the burned area, filled with epoxy, drilled a new hole, installed an extension wire to replace the relay pin burned below the PC level, and reinstalled." 

    This situation is extremely concerning. While I understand how this modification may appear to function properly—and may even be considered acceptable by the building owner—it presents a serious and unacceptable liability risk. Anyone who assumes responsibility for a system that has been altered in this manner becomes exposed to significant legal and financial consequences if any failure occurs, even one completely unrelated to the modification identified here. That risk alone can be catastrophic, potentially resulting in severe financial loss, loss of licensure, or criminal liability—all in the interest of saving a relatively small amount of money.

    Safety controls that are certified by a recognized testing agency are approved only as manufactured, and only when installed and maintained according to factory specifications. Once a control has been altered—by adding epoxy, additional wiring, solder, or any other non-approved modification—it is no longer covered by that certification. At that point, all liability transfers to the last individual who serviced the equipment, regardless of whether they performed or were even aware of the original unauthorized modification.

    This is the most alarming aspect of the situation. Even if I were to perform a routine and otherwise unrelated service—such as replacing a nozzle, a relief valve, or another component—I would be assuming full responsibility for the risks created by an improper modification that should never have been made in the first place.

    Max, this control must be replaced immediately with a properly listed and approved unit. This is not optional. Please obtain a replacement control as soon as possible.

    I think of my dealing with Lennox Industries on a job in Avalon NJ. Nothing to do with solving the problem but Lennox washed their hands of the job as a result of a modification I thought was just perfect. Read this post:

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MaxMercy
  • MaxMercy
    MaxMercy Member Posts: 570

    I appreciate your advice as always Ed, but there was no modification made to the control, only the repair of the printed circuit and the replacement of one pin of the relay. I should have taken some pictures (and I did think of that after I finished, but I was more concerned about pipes freezing). For some context, I am a retired electrical engineer that has designed and/or built hundreds of prototypes going back to the 1970s when I used to free hand resist draw, chemically etch, and drill prototype printed circuits.

    Worst case scenario is that it fails, the burner motor won't run again. The repair did not in any way alter the original design or affect the safeties in the controller (I pulled the yellow cad cell wire after I reinstalled the control and it locked out in 45 seconds). I will replace that controller as time permits with the Carlin controller because it features diagnostics and it's shorter lockout time, but I assure you the repair was proper and safe.

    Gabriel82
  • Gabriel82
    Gabriel82 Member Posts: 19

    Well, maybe I want to use the burner/heater boiler while on the move just on battery, 12 or 24 volt...

    As is, with AC I have to have a pure sine wave inverter with enough power "resistance"on top of what is the maximum that AC motor will draw(Amps)...

    And if I blow up in smoke the inverter I still cannot use the burner AND I need a new inverter...

    😑🤔

    not fun...

    Bad to the Bone

    Song by George Thorogood & The Destroyers ‧ 1982

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769

    @MaxMercy replied: I appreciate your advice as always Ed, but there was no modification made to the control

    So you are saying that the control comes from the factory with epoxy and wire identical to the epoxy and wire you provided? I think not.

    Perhaps I didn't make myself clear. The fact that your modification has nothing to do with a subsequent failure where there is a catastrophic failure (for instance a relief valve that fails to release and the a section of the cast iron explodes off the side of the boiler and damages property causes an injury or causes a death might happen**) will have no bearing on the insurance companies determination, the boiler manufacturer's determination or even the relief valve manufacturers determination that the problem was not their responsibility as a result of the unauthorized repair of the primary safety control.

    When in front of a judge… that went to law school and never picked up a wrench in her life, that has no practical knowledge of what we actually do for a living, and your background as an electrical engineer, … hears that you put wire and epoxy on a control that is called "The Primary Safety Control" from another lawyer… that has never picked up a wrench in her life, that has no practical knowledge of what we actually do for a living, and your background as an electrical engineer, and they see how much you are worth, …what do you think the judge will decide?

    I'm not saying you are wrong or did anything dangerous, I'm just giving you the facts from the several court cases I have been witness to.  The real world is out to get us MAX.  

    I don't believe you need to replace that control because you made the repair,  and in your situation I might have done the same thing.  The difference is that the next business day I personally would be purchasing the replacement control and installing it ASAP.  

    Just some ramblings of an old man with a wrench


    ** I actually saw a boiler in Stone Harbor NJ, with the relief valve outlet plugged to stop it from leaking, when giving an estimate for new equipment.  A few weeks later that same person asked me if I could fix the boiler and when I arrived a 12” x12”  section of cast iron was embedded into a cinder block wall next to the boiler.  I guess it over pressured as a result of a control defect and a relief valve that did not discharge the pressure that built up.   I was surprised at the sheetmetal cover of the boiler being torn away like you might see on a Saturday morning cartoon  

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MaxMercy
  • Gabriel82
    Gabriel82 Member Posts: 19

    I'm on it 😁

    Right now I do suspect two DC brushless motors would be needed!

    One for the oil pump and one for the combustion fan.

    I almost managed to buy a diesel heater that had two brushless motors(one for combustion fan ,other one for cooling the heat exchanger,since it's air heater).

    Someone else bought it faster than me...

    This setup is for higher efficiency since combustion fan/motor can run for optimum efficiency and the other one can have a higher rpm so that air can be circulated over the heat exchanger.

    So more energy is extracted from same quantity of fuel . Up to a point ,since diesel fuel needs some heat and air to burn properly!

    Brushless motors are small,can pack up Power, are adjustable by voltage, hell even electric bicycle have them...

    Why not an oil burner?

    Since the oil pump has a coupling part to fit the same motor that spins the centrifugal impeller.

    AND ,since you say it in a comment above ,a DC small voltage would be safer than 115AC, or 230AC...

    As for the ignition part ,well yeah, that still is dangerous...

    But ,I managed to shock myself in an old Bmw M20B20 plug wires...

    By accident... about 20000 volts 😂

    Hurt a bit.

    All I'm saying ,as history proved it ,even oil burners can be improved!

    Motors, Fans, combustion side, heat exchanger(condenser ones and corrosion resistant alloys, 316L, 904L, AL29-4C,etc...) .

    All for the benefit of the customer(who wants higher fuel bills or never ending parts orders?!).

    Bad to the Bone

    Song by George Thorogood & The Destroyers ‧ 1982

  • MaxMercy
    MaxMercy Member Posts: 570

    "So you are saying that the control comes from the factory with epoxy and wire identical to the epoxy and wire you provided? I think not."

    You're correct, it didn't come that way, but it is also in the realm of what is considered a proper printed circuit repair. It's analogous to sectioning a part of a rusted out automobile quarter panel and welding in a new patch panel.

    I get that the world is out to get us - we have more lawyers than doctors, and that gap continues to widen…

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769
    edited January 29

    @MaxMercy, Defending your experience and technical skills in a court of law, when someone was injured or worse, will fall on deaf ears. You are absolutely right as you are taken the the cleaners by some slick lawyer

    But you can feel better with the knowledge that I also agree with you. 

    Here's another story from 2013 where the person that is responsible for a disaster was not punished at all, but the innocent were to blame since they have deeper pockets.  That is how the legal system works here.

    https://whyy.org/articles/house/

    This happened in my neighborhood in 2013.

    1. An elderly couple switched from LP to Natural Gas.
    2. There was gas left in the LP tank
    3. The contractor that installed the new gas lines (Shore Guys) left the unused LP pipe in the crawlspace
    4. The propane company did not collect their LP tank in a timely manor
    5. The gas fireplace could not be converted to natural gas
    6. When the handyman Neighbor heard that there was gas left in the tank and that the fireplace gas log could still burn LP GAS, he did the friend a favor and tried to light up the fireplace by opening the valve on the abandoned gas tank.
    7. When that was unsuccessful because the LP Gas line was disconnected and abandoned under the home, he gave up and forgot to close the LP Tank valve
    8. The next time the well pump under the home sparked on, the house was gone!

    Who made the mistake? the neighbor. Who got blamed? the Contractor and the LP gas delivery company.

    But this won't happen to you MAX. That stuff happens to other people!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769

    @Gabriel82 says:

    I'm on it 😁

    Right now I do suspect two DC brushless motors would be needed!

    One for the oil pump and one for the combustion fan.

    You will need to redesign the fuel pump pressure regulator or have an electronic orifice size adjusting mechanism.  That is because changing the speed the fuel pump rotates does not change the pressure sent to the nozzle.  

    If the fuel pump rotates too slowly, the pressure valve will not open at all, which means that there will be no fuel at low fire speed.  So how will that work for you?  Low fire = No fire

    Once the pump rotation speed reaches the minimum speed to open the pressure regulating valve you will get the fuel at the pressure that adjustment is set for.  (100 PSI For example)  As you increase the pump motor speed the pump gears will force more oil into the pressure regulating chamber and the pressure regulating device will continue to deliver 100 PSI pressure to the nozzle, and all the other oil will be bypassed back to the tank or the inlet of the pump. 

    So the faster you go, the more air you will force into the combustion chamber, the more oil will be bypassed to the tank or pump inlet, but the amount of oil will remain the same as a result of the pressure regulator in the pump being set at 100 PSI and the nozzle orifice being fixed at the same GPH rating no matter what pump motor or the fan speed is turning.    


    But What do I know?

    If it were that easy, someone would have already done it!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HydronicMike
    HydronicMike Member Posts: 297

    Dead spots can be checked with a multimeter, as can the start switch on a split phase motor.

    Intplm.
  • HVACNUT
    HVACNUT Member Posts: 7,312

    I've been reading your posts for at least a few years now. So I KNOW you're not crazy. Why would you go through all that nonsense on an obsolete control, when an upgrade doesn't break the bank, and would be superior in so many ways? Its puzzling to me.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,914

    You can do whatever you want regarding controls repair, re solder or whatever monkey business you want. If something happens you will be responsible

    Those of us that went to some type of trade school and obtained heating, AC or electrical licenses basically were forewarned not to monkey with safety controls and control repairs. It's not worth it or the liability involved.

    No matter what good intentions you have the judge will put you away.

    I have an example:

    In the old days before many electronics vacuum tubes were common in burner controls. Honeywell had the RA890 burner control used on oil or gas burners (commercial) Common in the 50s & 60s

    One fault this control had was that a match book was the perfect size to hold the flame relay closed to keep the burner running instead of locking out. Not good but that's not my story.

    Honeywell specified that you should only use Honeywell vacuum tube #####. That being said when you needed tubes you just went to the electronics store and bought a tube that crossed referenced over. For all practical purposes it was the same exact tube.

    But not as far as a Judge and Honeywell were concerned. There were many burner failures that Honeywell got out of because of a substituted tube

  • Gabriel82
    Gabriel82 Member Posts: 19

    Can someone tell me if these motor/rotor problems happen in the 24V dc beckett burner?

    Around here,in Romania Riello and some german brands(with blue flame low nox) are the most seen in oil or natural gas boilers.

    In all honesty I haven't even seen a Beckett burner.

    Although the way is designed seems a lot simpler to service than many other brands!

    Thank you!