F&T trap on return drop
ACS
ACS Member Posts: 6
Hi! I have a 2 pipe steam system (see first pic) and 2 return pipes coming back (see second pic ZOOM UP). On the ZOOM UP pic, you can see that the plumber removed an F&T trap (you see tape marking on two pipes) and replaced it with a copper air vent - this was done 3 years ago. I'm recently noticing two problems w the heating - the return pipe on the right is getting hot and the boiler is constantly cycling to hit thermostat temp (it does turn off but turns on again within 1 minute, til we hit thermostat temp). Could the removal of the F&T (replaced by air vent) be contributing to the problems i am having? I've also added a pic of the F&T from when it was removed. THANKS ALL!
    Jamie Hall Member Posts: 27,355
    Oh my. That was, once upon a time, a vapour system — operating silently and evenly on no pressure at all to speak of.
    I wonder what else has been kludged over the years…
    Ii also wonder what the venting is now. And the condensate return.
    And how much oversize the boiler is…
    Where are you located? This really needs a steam person to take a look and see what is happening.
  • ACS
    ACS Member Posts: 6
    long island
  • guzzinerd
    guzzinerd Member Posts: 457
    edited January 27
    Exact same thing was done to my 2 pipe system but with a MoM vent. I replaced it (was leaky) with a gorton #4, fixed the crossovers traps and increased the venting on the mains. Runs at less then 5inch pounds now. Not really a vapor system anymore but seems happy since the vaportrol never needs to cycle it down.
    Found the original 220, in the crawlspace, I've thought about restoring
    Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
    Steamhead Member Posts: 18,489
    @ACS , that wasn't an F&T trap. It was a "vent trap" or "float trap/air eliminator" designed to keep water from escaping from the system, to vent the air and possibly to hold vacuum.
    The vent they used is a Hoffman #74, which has a very small vent port. I'd replace it with a Gorton #2, which vents much, much faster.
    Consulting
  • ACS
    ACS Member Posts: 6
    @Steamhead, thanks… but could the old f&t trap have been serving a purpose other than removing air? should i revert back to f&t? also, if i still go with gorton #2, does the location matter? note: old f&t had inlet at top of returns, and outlet at bottom of returns (you can see tapemarks for old f&t placement in the first pic)… tx
    mattmia2 Member Posts: 16,736
    it wasn't an f&t trap, it was a special vent trap for a vapor system.
    do all the emitters heat? if the emitters are all mostly hot it is cycling on pressure because the boiler is too big. you can add a time delay to delay the cutin a bit when the vaporstat shuts the boiler off if everything else is ok other than the short cycling.
  • ACS
    ACS Member Posts: 6
    ah, got it. i have 9 emitters. of these, 3 of them ONLY heat on one side (always supply side). all others heat ok. thanks mattmia2.
    Replace the Hoffman vent with the Gorton #2 and everything should heat faster.
    Consulting
  • ACS
    ACS Member Posts: 6
    edited February 9
    @Steamhead , i picked up the gorton no 2 but am seeing that it is 1/2". i have a 3/4" pipe where the current hoffman no 74 is. will an elbow reducer (from 3/4 to 1/2) cause any issues or reduce effectiveness of the gorton? THANKS!
    No, but a 3/4x1/2" bushing screwed into the existing 90 will do the job as well.
    Consulting
