high efficiency with multiple problems long flue
jdfinch
jdfinch Member Posts: 1
i have a high efficiency that was installed. constantly goes through pressure switches. and does kick on till there is a 20 degree differential. flue comes out end 2" for 12in 90's 12in then adapts up to 4 inches. travels 30 feet 90's travels 15 feet 90's travels 5 ft 90's up and out of the building. i did add a saddle on the 4" about a foot from the transition. it has 1"1/2 pipe down about 16 inches to a trap and empties into a bucket. just trying to stop the condensate from flooding the furnace and taking out the pressure switch. i need advice short of calling a company and having it replaced.
    pecmsg Member Posts: 7,053
    The IOM will have specific ways of running that vent and how to drain.
  • Ironman
    Ironman Member Posts: 7,903
    Unless that’s a 400k btu appliance, a 4” pipe is too large and will cause excessive condensation and venting issues.
    What size boiler do you have?
    How about posting some pics of the boiler and venting?
    Bob Boan
    Mad Dog_2
    hot_rod Member Posts: 27,445
    The installation manual should have the venting sizing table. Lengths, fitting equivalents etc.
    GGross
