Ghost flow help please
13»
  • Grallert
    Grallert Member Posts: 1,068
    can you hear the offending flocheck close when the circ stops? Very often they make a distinctly metallic tap when the weight falls to the seat.
    HVACNUT Member Posts: 7,296
    I don't think I've ever heard the sound of a Flo valve seat. I've definitely heard them chatter.
    My bet is the same zone gets the ghost flow after the swap. Spring Check on the return, or zone valve as @EBEBRATT-Ed suggested.
    This is fun when I'm not there.
    bjohnhy
    EBEBRATT-Ed Member Posts: 19,840
    We can talk about it forever. A zone valve.
  • bjohnhy
    bjohnhy Member Posts: 177
    @Barley12 can you tell us the rise or the elevation difference from the boiler to the highest point of zone 1 (presumable the baseboard a radiators). If its 2 stories above your basement, that would be about 18 ft? What about the other zones?
  • Barley12
    Barley12 Member Posts: 50
    didn't get a chance to swap them today but hopefully tomorrow
  • Big Ed_4
    Big Ed_4 Member Posts: 3,404
    3/4" flow checks are too small and problematic with any rise . The lighter weight and smaller seat could be the issue .. A basement zone not a problem .. The 1" flow check would be the safest to install … Next time around
    Barley12
    hot_rod Member Posts: 26,989
    the pump second from left looks like a late model. It might take an internal check, check with Taco. Move it to the problem zone.
    That would be a$40.00 fix.
    Big Ed_4
  • Barley12
    just swapped them…..time will tell
    bjohnhy
  • Barley12
    Zone 1 is on the 2nd floor. The pipe has a 55' run in the basement then goes up 2 stories.
  • Barley12
    2nd pump from the left is new. I replaced it a month or so ago. I do not believe it has an internal Flocheck but could be wrong.
  • Barley12
    new pump says 007-F5
  • Barley12
    zones 1,2,3 all rise to second floor. Zone 4 is first floor. Zone 5 is hot water tank
    Swapped flow checks or the new pump to the problem zone?
  • Barley12
    just the flochecks to start with. Want to see if the problem moves.
    Did you swap the whole valve, or just the inserts?
  • Barley12
    I swapped the entire valve….super quick/easy to swap.
  • Barley12
    so I'm out of town but the first 24 hours the temp held steady. I'll report back on Monday night.
    bjohnhyhot_rod
  • Barley12
    All temps held at 60 degrees while I was out of town. The g flow seems to have stopped since I swapped the flochecks. I'll continue to monitor.
    bjohnhyHVACNUT
  • Barley12
    Still holding strong. I guess the new flowcheck wasn't strong enough for zone 1 but surprisingly it is holding on zone3.
    bjohnhy