can you hear the offending flocheck close when the circ stops? Very often they make a distinctly metallic tap when the weight falls to the seat.
Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver
0 -
I don't think I've ever heard the sound of a Flo valve seat. I've definitely heard them chatter.
My bet is the same zone gets the ghost flow after the swap. Spring Check on the return, or zone valve as @EBEBRATT-Ed suggested.
This is fun when I'm not there.
1 -
We can talk about it forever. A zone valve.
0 -
didn't get a chance to swap them today but hopefully tomorrow
0 -
-
the pump second from left looks like a late model. It might take an internal check, check with Taco. Move it to the problem zone.
That would be a$40.00 fix.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
Zone 1 is on the 2nd floor. The pipe has a 55' run in the basement then goes up 2 stories.
0 -
2nd pump from the left is new. I replaced it a month or so ago. I do not believe it has an internal Flocheck but could be wrong.
0 -
new pump says 007-F5
0 -
zones 1,2,3 all rise to second floor. Zone 4 is first floor. Zone 5 is hot water tank
0 -
Swapped flow checks or the new pump to the problem zone?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
just the flochecks to start with. Want to see if the problem moves.
0 -
Did you swap the whole valve, or just the inserts?
0 -
I swapped the entire valve….super quick/easy to swap.
0 -
-
-
-
g flow returned today. It was good for almost a month.
0 -
it has to be related to that Flocheck but just not sure what to do now.
0 -
did you swap the entire valve, or are you removing just the internals and swapping them?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
I will put in circular pump with a built-in flow heck to see if that does it. That is a simple swap
0 -
I swapped the entire flow valve
0 -
-
still holding strong.
0 -
I looked at this entire 3 page thread. I looked at the photos I see one Taco SR503 and one Taco SR501. That would account for 4 circulator pumps. You have 5 circulator pumps Where does the other circulator pump get connected? where does that circulator's thermostat get connected? You may be looking in the wrong place to solve this problem.
I would like to see the inside wiring on your Aquastat relay if you can take a picture of that. maybe move the wires a little so I can see the terminal designations on that aquastat relay control.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements