Ghost flow help please
Comments
-
can you hear the offending flocheck close when the circ stops? Very often they make a distinctly metallic tap when the weight falls to the seat.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
I don't think I've ever heard the sound of a Flo valve seat. I've definitely heard them chatter.
My bet is the same zone gets the ghost flow after the swap. Spring Check on the return, or zone valve as @EBEBRATT-Ed suggested.
This is fun when I'm not there.
1 -
We can talk about it forever. A zone valve.
0 -
didn't get a chance to swap them today but hopefully tomorrow
0 -
3/4" flow checks are too small and problematic with any rise . The lighter weight and smaller seat could be the issue .. A basement zone not a problem .. The 1" flow check would be the safest to install … Next time around
There was an error rendering this rich post.
0 -
-
-
Zone 1 is on the 2nd floor. The pipe has a 55' run in the basement then goes up 2 stories.
0 -
2nd pump from the left is new. I replaced it a month or so ago. I do not believe it has an internal Flocheck but could be wrong.
0 -
new pump says 007-F5
0 -
zones 1,2,3 all rise to second floor. Zone 4 is first floor. Zone 5 is hot water tank
0 -
Swapped flow checks or the new pump to the problem zone?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
just the flochecks to start with. Want to see if the problem moves.
0 -
Did you swap the whole valve, or just the inserts?
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements