Ghost flow help please
13»
  • Grallert
    Grallert Member Posts: 1,118
    can you hear the offending flocheck close when the circ stops? Very often they make a distinctly metallic tap when the weight falls to the seat.
    HVACNUT Member Posts: 7,450
    I don't think I've ever heard the sound of a Flo valve seat. I've definitely heard them chatter.
    My bet is the same zone gets the ghost flow after the swap. Spring Check on the return, or zone valve as @EBEBRATT-Ed suggested.
    This is fun when I'm not there.
    bjohnhy
    EBEBRATT-Ed Member Posts: 20,180
    We can talk about it forever. A zone valve.
  • bjohnhy
    bjohnhy Member Posts: 206
    @Barley12 can you tell us the rise or the elevation difference from the boiler to the highest point of zone 1 (presumable the baseboard a radiators). If its 2 stories above your basement, that would be about 18 ft? What about the other zones?
  • Barley12
    Barley12 Member Posts: 57
    didn't get a chance to swap them today but hopefully tomorrow
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    3/4" flow checks are too small and problematic with any rise . The lighter weight and smaller seat could be the issue .. A basement zone not a problem .. The 1" flow check would be the safest to install … Next time around
    Barley12
    hot_rod Member Posts: 27,468
    the pump second from left looks like a late model. It might take an internal check, check with Taco. Move it to the problem zone.
    That would be a$40.00 fix.
    Big Ed_4
  • Barley12
    just swapped them…..time will tell
    bjohnhy
  • Barley12
    Zone 1 is on the 2nd floor. The pipe has a 55' run in the basement then goes up 2 stories.
  • Barley12
    2nd pump from the left is new. I replaced it a month or so ago. I do not believe it has an internal Flocheck but could be wrong.
  • Barley12
    new pump says 007-F5
  • Barley12
    zones 1,2,3 all rise to second floor. Zone 4 is first floor. Zone 5 is hot water tank
    Swapped flow checks or the new pump to the problem zone?
  • Barley12
    just the flochecks to start with. Want to see if the problem moves.
    Did you swap the whole valve, or just the inserts?
  • Barley12
    I swapped the entire valve….super quick/easy to swap.
  • Barley12
    so I'm out of town but the first 24 hours the temp held steady. I'll report back on Monday night.
    bjohnhyhot_rod
  • Barley12
    All temps held at 60 degrees while I was out of town. The g flow seems to have stopped since I swapped the flochecks. I'll continue to monitor.
    bjohnhyHVACNUT
  • Barley12
    Still holding strong. I guess the new flowcheck wasn't strong enough for zone 1 but surprisingly it is holding on zone3.
    bjohnhy
  • Barley12
    g flow returned today. It was good for almost a month.
  • Barley12
    it has to be related to that Flocheck but just not sure what to do now.
    did you swap the entire valve, or are you removing just the internals and swapping them?
  • bjohnhy
    I would install that spring check valve on the return side since you have more pipe there to work with.
    Alternatively…. you can swap the taco circulators around so you can use the IFC internal flow check valve on that new circulator on the problem zone.
    Intplm.
  • Barley12
    I will put in circular pump with a built-in flow heck to see if that does it. That is a simple swap
  • Barley12
    I swapped the entire flow valve
  • Barley12
    got a new circulator pump with IFC and installed it last night. Everything is good this morning. I find it odd that every time I have put in a new flow check it works for a few days and then fails. The last swap for an old flow check valve worked for a month and then failed.
    bjohnhy
  • Barley12
    still holding strong.
    EdTheHeaterMan Member Posts: 12,190
    I looked at this entire 3 page thread. I looked at the photos I see one Taco SR503 and one Taco SR501. That would account for 4 circulator pumps. You have 5 circulator pumps Where does the other circulator pump get connected? where does that circulator's thermostat get connected? You may be looking in the wrong place to solve this problem.
    I would like to see the inside wiring on your Aquastat relay if you can take a picture of that. maybe move the wires a little so I can see the terminal designations on that aquastat relay control.
  • Barley12
    still holding proper temps for over a month now.
    To the above question…….the 5th circ pump on a hot water storage tank w its own stat/temp control dial on top of the storage tank.
    bjohnhy
