Expansion tank install
I am going to be installing a new furnace that will include a new expansion tank and air scoop as in the diagram. Obviously, I am going to have to drain down the whole system beforehand. Now the water side of the blader type expansion tank is going to have a lot of air in it. Is there a fast and easy way to get all of the air out of the tank when I fill the system back up with water? And from what i recall there must be a minimum length of pipe between the furnace and the air scoop and expansion tank. is that right?
" Now the water side of the blader type expansion tank is going to have a lot of air in it. "
Gravity.
One Pipe System0 -
The system will need to be purged of air. And your diagram is not showing a purge station.
@scatgo If you use a air scoop as pictured, you need an eighteen inch nipple before the air scoop. If you use a micro bubble air separator, (in my opinion a better product) an eighteen inch nipple/length of pipe is not required. I would use a micro bubble air separator, a much better air eliminator than an air scoop as in your drawing.
The bladder type expansion tank is commonly pre-charged to the system pressure requirements. On a Hot water boiler that pressure would be 12-15 psi, the same as your automatic feed valve. I like that you have the feed valve at the point of no pressure change.
One thing I like to do is add a valve between the expansion tank and the tee. This helps tremendously when the expansion tank needs to be replaced (and it will need replacement).
The way to purge a new system requires a purge tee set up preferably on each zone. Here is a picture one example a purge tee. There are others you can use too.
This is the system i will be dealing with.
the link
Living the hydronic dream0