Expansion tank install

Options
scatgo
scatgo Member Posts: 75
edited January 4 in THE MAIN WALL

I am going to be installing a new furnace that will include a new expansion tank and air scoop as in the diagram. Obviously, I am going to have to drain down the whole system beforehand. Now the water side of the blader type expansion tank is going to have a lot of air in it. Is there a fast and easy way to get all of the air out of the tank when I fill the system back up with water? And from what i recall there must be a minimum length of pipe between the furnace and the air scoop and expansion tank. is that right?

extrol__70106.jpg

Comments

  • 109A_5
    109A_5 Member Posts: 3,543

    " Now the water side of the blader type expansion tank is going to have a lot of air in it. "

    Gravity.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jamie Hall
    Jamie Hall Member Posts: 26,887

    When you pressurizejthe expansion tank to system pressure before you attach it to the system, that will drive all the water out of it.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Grallertscatgo
  • hot_rod
    hot_rod Member Posts: 26,742

    consider upgrading to a micribubble type air purger. The work faster and better than the scoop type, with no dimension limitations

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    scatgoHydronicMikeGGross
  • HVACNUT
    HVACNUT Member Posts: 7,267

    The system will need to be purged of air. And your diagram is not showing a purge station.

  • hot_rod
    hot_rod Member Posts: 26,742
    Screenshot 2026-01-04 at 8.59.36 AM.png

    A Webstone valve here allows you to isolate the components, pump, expansion tank. And also drain pressure off the expansion tank if it ever needs replacement, since the purge port can work on either side of the ball shut off valve.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    HydronicMike
  • Intplm.
    Intplm. Member Posts: 2,850

    @scatgo If you use a air scoop as pictured, you need an eighteen inch nipple before the air scoop. If you use a micro bubble air separator, (in my opinion a better product) an eighteen inch nipple/length of pipe is not required. I would use a micro bubble air separator, a much better air eliminator than an air scoop as in your drawing.

    The bladder type expansion tank is commonly pre-charged to the system pressure requirements. On a Hot water boiler that pressure would be 12-15 psi, the same as your automatic feed valve. I like that you have the feed valve at the point of no pressure change.

    One thing I like to do is add a valve between the expansion tank and the tee. This helps tremendously when the expansion tank needs to be replaced (and it will need replacement).

    The way to purge a new system requires a purge tee set up preferably on each zone. Here is a picture one example a purge tee. There are others you can use too.

    shopping.jpeg
    scatgo
  • scatgo
    scatgo Member Posts: 75

    This is the system i will be dealing with.

  • Intplm.
    Intplm. Member Posts: 2,850

    @scatgo Please resend this link. It does not open/shows a black screen only.

  • hot_rod
    hot_rod Member Posts: 26,742
    IMG_1752.jpeg

    the link

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream