Hyper heat not reaching heat set temp if below 35
day2dive
day2dive Member Posts: 5
i have a new Mitsubishi SUZ-AA36NL heat pump that will not maintain or reach set temp if outdoor temp is 35 or lower .
the air handler is SVZ-AP36NL. My installer has been out twice, once found thermostat wired wrong, the other time said a wiring issue with AH. Neither has “fixed” the issue.
go to bed ..set at 72; indoor temp 74( using fireplace at night)
Wake up to 65 , unit running all night , outdoor temp 30.
TIA for anything I can suggest to them
  • Ironman
    Ironman Member Posts: 7,903
    It’s probably not charged correctly. There are strict guidelines in the installation manual for how much additional charge is required depending on the indoor unit(s), branch box(es) line set lengths, etc. Most installers have trouble with them, but the distributor can also calculate them with Mitsubishi’s Diamond software if given the correct info.
    The only way to properly charge the system is to weigh the correct amount in; it can’t simply be “topped off” by guessing or taking superheat and sub cooling readings.
    If the contractor has already added refrigerant, but didn’t do it using the proper calculations, then it all has to be removed and the proper amount weighed in based upon the proper calculations.
    Bob Boan
    day2divebjohnhy
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    Do you have the option for an auxiliary back up ? I will always recommend for the cold nights ….
    EBEBRATT-Ed Member Posts: 20,164
    edited December 2025
    Another unhappy HP customer.
    @day2dive where are you located? Cold climate?
    Steamheadkcopp
  • day2dive
    not particularly cold climate…Tennessee……
    I would think a HP should work in Tn.
    I would call the service manager or the owner and have a heart to heart with them. You paid for something that should work and it doesn't. Since it fails below 30 I am guessing in may be a defrost issue but my guess means nothing. They need to go through the unit and make it right. Mitsubishi is good equipment if installed right.
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,241
    Call them back, they need to fix it. I have a hyper heat that works when it’s below 10F.
  • yellowdog
    yellowdog Member Posts: 293
    This all comes down to what is your heat loss versus the output of the air handler at the temperature you say it stops working at. Without this information, you will just be guessing at a fix. You need a heat loss done on the space the air handler serves and a diamond system builder report of what the output of the system is so you can see if it is a capacity, installation or charge issue.
  • day2dive
    thanks for all the suggestions
    I’m …pushing….for them to check the charge ….
  • Ironman
    Well, unfortunately that’s the issue that I tried to explain. There’s no real way to accurately “check the charge”. If wasn’t properly calculated and weighed in, then it’s wrong.
    You need ask them if it was calculated according to the manual and to show the calculated amount.
    Bob Boan
    GGross
    pecmsg Member Posts: 7,053
    3-Tons, how was that decided?
    Has the charge been pulled and weighed? That’s the only way to know if it’s correct!
    was this by dealer?
  • day2dive
    installer…pulled charge and weighed it and said it was correct for line length…will replace it and check other items
    installer is new to these units but. Is a Mitsubishi dealer ….just hyper heat is rarely installed in Tenn apparently
    Thanks for all the suggestions …thus far
    I’m hoping someone from Mitsubishi may offer some guidance
    If the charge is correct reinstall and contact tech support.
    I highly recommend an ICM493 voltage monitor surge protection.
    Big Ed_4
  • day2dive
    i have a whole house surge protector …sufficient I hope but, thank you
    get the ICM!
    Whole House is 1shot.
    doesn’t inform you it’s over?
    The ICM is 5, when 4 are used it alerts it at the end.
    IronmanBig Ed_4
  • yellowdog
    @day2dive Still need to verify the heat loss versus the output. Is the ductwork sized correctly for the house and the system?
    -30 ambient will be -40 coil. There will be a lot of defrosting
  • DCContrarian
    DCContrarian Member Posts: 1,457
    You need to establish which of these two cases is happening:
    1. The heat pump is not producing its rated output; or
    2. The heat pump is working as designed but is undersized to meet your heating load.
    It's two completely different sets of solutions.
    IronmanyellowdogHot_water_fan
  • GGross
    GGross Member Posts: 1,882
    This is a ducted unit? the issues could be related to delivery (the ductwork)