Calculating heat loss
magewick
magewick Member Posts: 31
heat loss radiation survey - should radiator covers and uninsulated main piping be included in the survey
    hot_rod Member Posts: 27,507
    just the structure itself, walls, windows, roof, etc.
    All homes have some internal gains from lighting, perplexing, appliances, etc.
    ethicalpaul Member Posts: 8,863
    are you trying to size a steam boiler with this information?
  • magewick
    Yes - trying to size boiler
    Jamie Hall Member Posts: 27,397
    A steam boiler is not, repeat NOT, sized by building heat loss. It must be sized to match the installed radiation.
    A hot water boiler is sized by heat loss, but not to exceed the installed radiation — quite a significant difference in many cases.
    Which are you doing?
    EBEBRATT-Ed Member Posts: 20,236
    If it is steam the radiation rating (total) determines the size of the boiler. Simply determine the radiation load in EDR or square feet (same thing) and compare that to the boiler rating in square feet of steam.
    Don't calculate BTUs you will just get confused.
    The boiler rating in square feet already has an allowance for piping and pick up built in