Wiring Weil-McLain AquaPlus to a Taco SR503-5

Options
JS41190
JS41190 Member Posts: 14

I have a Weil-McLain CGa 5, Weil McLain Aqua Plus 45 and Taco SR503-3.

I am trying to wire the Indirect’s aquastat to the Taco SR. I have both of the inputs on the aquastat getting 24V from the R and W terminals in the Taco SR. (There is no display on the aquastat).
Where would I wire the OUTPUT of the aquastat to on the Taco SR? I am thinking the X X Priority End Switches, but I do not want to destroy either of these controls obviously.

IMG_4162.jpeg IMG_4163.jpeg

Comments

  • Ironman
    Ironman Member Posts: 7,874
    edited December 19

    No, the end switch is what brings the boiler on.

    You wire the aquastat to the priority zone terminals “R & W”.

    “AC1 & AC2” go to the “24V” terminals.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    HydronicMike
  • 109A_5
    109A_5 Member Posts: 3,483
    edited December 20

    For DHW priority.

    Red on the aquastat to R Zone 1 (priority) on the zone panel.

    White on the aquastat to W Zone 1 (priority) on the zone panel.

    Yellow on the aquastat (AC1) to Zone 1 (priority) C on the zone panel. (AC1 shows it as the grounded side)

    Green on the aquastat (AC2) to R on the zone panel.

    Enable the priority, the switch array on the Right hand side.

    Connect the Main X-X and Priority X-X (DHW) End Switch terminals to the appropriate place on the boiler.

    Connect the heating zones to Zone 2 and Zone 3.

    Make sure the circulators are wired appropriately.

    image.png image.png

    image.png

    image.png image.png